Sir

I have 230 v UPS system,I need 110v supply .

Then I connect 230v/110v transformer in UPS output ( transformer secondary no load connected ).
Now UPS output tripped and display fault indication.

then i removed transformer and connect hologen lamp 1000w UPS working well.

Why?

Thank you,
 

duke37

Jan 9, 2011
5,364
Joined
Jan 9, 2011
Messages
5,364
A transformer takes a considerable inductive current which could be the cause of the trouble.
A better configuration would be to transform the mains down to 110V and then use a 110V in/out UPS.
 

sudhakar

Jun 19, 2017
20
Joined
Jun 19, 2017
Messages
20
A transformer takes a considerable inductive current which could be the cause of the trouble.
A better configuration would be to transform the mains down to 110V and then use a 110V in/out UPS.