Hi Guys,

I need someone to help me design a schematic for a basic relay driver (24VDC feed from PLC into optocoupler, which drives a relay). Pretty basic, but my main question is around the relay.

The relay needs to switch 240VAC loads (up to 2400W / 10A). Is it possible / safe to have the relay mounted on PCB and be able to handle this sort of current, or would I be better off using an externally mounted relay?

Thanks in advance,

Ben.
 

davenn

Moderator
Sep 5, 2009
14,260
Joined
Sep 5, 2009
Messages
14,260
The relay needs to switch 240VAC loads (up to 2400W / 10A). Is it possible / safe to have the relay mounted on PCB and be able to handle this sort of current, or would I be better off using an externally mounted relay?

Hi Ben

there are proper SSR ( Solid State Relays) available for this sort of thing. I would strongly suggest you get one of those
It will simplify your project and be a hell of a lot safer :)

google 240V switching SSR's

Dave
 

Minder

Apr 24, 2015
3,478
Joined
Apr 24, 2015
Messages
3,478
Another solution is to use a contactor, these are traditionally a large form of a relay so it would be mounted separate to any PCCT board.
M.
 

AnalogKid

Jun 10, 2015
2,893
Joined
Jun 10, 2015
Messages
2,893
With proper attention to trace width and copper thickness (weight), a pc board design can handle your voltage and current easily. After all, they are common in many power supplies.

Since a relay has true galvanic isolation, why do you have an optocoupler between it and the PLC? Very few optos can move the current needed by the coil of a relay with those contact ratings.

ak
 

Tha fios agaibh

Aug 11, 2014
2,252
Joined
Aug 11, 2014
Messages
2,252
Why not just buy relays with 24vdc coil?

Btw, If your plc output card has common terminals for internal contacts, you can feed it with other than 24vdc.
Example; feed common terminal with 120v so it outputs 120v. Of course you need to observe its rating.
 

davenn

Moderator
Sep 5, 2009
14,260
Joined
Sep 5, 2009
Messages
14,260
Why not just buy relays with 24vdc coil?

Btw, If your plc output card has common terminals for internal contacts, you can feed it with other than 24vdc.
Example; feed common terminal with 120v so it outputs 120v. Of course you need to observe its rating.

he's dealing with higher voltage and significant current

SSR's are a very way to handle that
 

Tha fios agaibh

Aug 11, 2014
2,252
Joined
Aug 11, 2014
Messages
2,252
he's dealing with higher voltage and significant current SSR's are a very way to handle that

I agree, but SSR's can get expensive and they tend to fail more often than a mechanical relay.
A relay or contactor (coil) that matches the PLC output voltage is usually the best plan.

I wasn't suggesting attaching the load directly to the PLC output card. I was merely noting that a PLC can often be rewired to suit the output voltage desired for a relay that one might already have on hand.
 

Ben Halicki

Sep 3, 2015
10
Joined
Sep 3, 2015
Messages
10
Hi guys,

Thanks very much for the suggestions. Sounds like using a SSR might be the way to go.

Out of interest... the current measures around 9.6A. If I have a 10A relay, to me that is probably too close to the upper limit of the relay, but interested to hear your thoughts. Apologies in advance for digging up an old thread, I thought i'd posted this a while ago but apparently not :)
 

AnalogKid

Jun 10, 2015
2,893
Joined
Jun 10, 2015
Messages
2,893
The standard rule of thumb for electronic components (overrate everything by 100%) applies in part to an SSR. For a 10 A output current, use a 20 A part. You do not have to overrate the voltage spec, because an SSR with a max output rating of 240 Vac is designed to handle that continuously.

ak
 

Minder

Apr 24, 2015
3,478
Joined
Apr 24, 2015
Messages
3,478
I need someone to help me design a schematic for a basic relay driver (24VDC feed from PLC into optocoupler, which drives a relay).
The relay needs to switch 240VAC loads (up to 2400W / 10A). Is it possible / safe to have the relay mounted on PCB and be able to handle this sort of current, or would I be better off using an externally mounted relay?
.

Re-reading the OP, why exactly are you using a Opto coupler from the output of a PLC to drive a relay/contactor?
Why not drive the SSR or relay direct from PLC output?
I see it was suggested in #4