We have a large industrial motor that draws up to 50 AC amps that we need to
monitor in the control room 100 feet away. Looks like a current
trransormer takes our 50A and drops it to a 5A (full scale) level, which we
would run to a panel meter. I'm not sure this is a good way to go. Perhaps a
"permanent" clamp-on amp meter that outputs something besides mA-A signals
would be better? Looking for suggestions...thx
 
T

Tom Woodrow

Jan 1, 1970
0
you could use a meter with both a clamo-on amp meter and an RS232
interface and set it up to poll the meter up on a regular basis.

Tom Woodrow
 
D

Dimitrij Klingbeil

Jan 1, 1970
0
ltj said:
We have a large industrial motor that draws up to 50 AC amps that we need to
monitor in the control room 100 feet away. Looks like a current
trransormer takes our 50A and drops it to a 5A (full scale) level, which we
would run to a panel meter. I'm not sure this is a good way to go. Perhaps a
"permanent" clamp-on amp meter that outputs something besides mA-A signals
would be better? Looking for suggestions...thx

There are some pretty inexpensive Hall-effect-based current to voltage
converters available. They tend however to be a little inexact. You did not
tell what you need the data for. If it is just to see if some known and
constant level(s) has (/have) been exceeded, the easiest solution would
probably be such a sensor connected to a (/multiple) comparator(s) with the
inverse input on the needed fixed level(s). When the limit is reached, the
comparator will output series of 50Hz pulses that can easily be used to
trigger some sort of monitoring circuitry. The duty cycle of these pulses
will also provide a rough overview of how far the limit has been exceeded.
More exact current measurements are also possible, but you will need
converters that do not 'drift' too much. A current transformer will also
work, but with considerably higher losses due to heating.

Dimitrij
 
S

Steve

Jan 1, 1970
0
If all you need it a method to read the current on an anolog meter, there
are pick up loops that you just put on the motor lead and the loop windings
measure the field going through that lead.. Very easy to hook up to a remote
meter..

Just check with a industrial electrical supply house.

Steve
 
L

Luhan Monat

Jan 1, 1970
0
ltj said:
We have a large industrial motor that draws up to 50 AC amps that we need to
monitor in the control room 100 feet away. Looks like a current
trransormer takes our 50A and drops it to a 5A (full scale) level, which we
would run to a panel meter. I'm not sure this is a good way to go. Perhaps a
"permanent" clamp-on amp meter that outputs something besides mA-A signals
would be better? Looking for suggestions...thx
Running large amounts of current over that distance is not usually a
good idea. Put a 'current to voltage' transformer (little xformer with
large hole in the middle) over one of the AC wires and connect a
voltmeter remotely. Now you have only low voltage, low current running
back to the control room. Use a voltmeter and the specified load for
the transformer to read the current.
 
J

John Popelish

Jan 1, 1970
0
ltj said:
We have a large industrial motor that draws up to 50 AC amps that we need to
monitor in the control room 100 feet away. Looks like a current
trransormer takes our 50A and drops it to a 5A (full scale) level, which we
would run to a panel meter. I'm not sure this is a good way to go. Perhaps a
"permanent" clamp-on amp meter that outputs something besides mA-A signals
would be better? Looking for suggestions...thx

The low tec way to do this is just as you have described, using a pair
of 14 ga wires. If you want to go higher tech, get an AC current to
4-20 ma transmitter and read that signal with a scalable numeric
display. Yokagowa makes a display that includes the 24 volt supply to
power the transmitter over the signal wires (called a two wire
transmitter) with an AC power connection at the meter. But lots of
companies make the transmitters and displays. If you suspect that you
might ever want to connect this signal to a DCs or other industrial
control system, its input can be driven in series with the panel
display.
 
J

John Fields

Jan 1, 1970
0
Running large amounts of current over that distance is not usually a
good idea. Put a 'current to voltage' transformer (little xformer with
large hole in the middle) over one of the AC wires and connect a
voltmeter remotely. Now you have only low voltage, low current running
back to the control room. Use a voltmeter and the specified load for
the transformer to read the current.

---
There is no such thing as a "current to voltage converter" transformer.

What you're describing is using what's called a "current transformer"
and a "burden resistor" to generate an AC voltage which is proportional
to the current flowing in the primary, which is the single wire running
through or looped through the center of the toroidal core.

Using it as you've described is _not_ a good idea in that if the
secondary circuit is broken anywhere along the 200 feet of cable high
voltage will appear at the break.

Nor would it be a good idea to place the burden resistor directly across
the secondary unless the resistance of the volmeter and the run of wire
is taken into consideration.

More appropriate would be the use of a 4-20mA transmitter and receiver
as John Popelish has suggested.
 
W

Watson A.Name - Watt Sun, Dark Remover

Jan 1, 1970
0
Running large amounts of current over that distance is not usually a
good idea. Put a 'current to voltage' transformer (little xformer with
large hole in the middle) over one of the AC wires and connect a
voltmeter remotely. Now you have only low voltage, low current running
back to the control room. Use a voltmeter and the specified load for
the transformer to read the current.

There is no need to run currents over that distance. If the shunt is
located at the motor, then 49.999 amps go thru the shunt, and only 1
mA (assuming a 1 mA meter movement) has to travel remotely to the
meter. If the meter is insulated and the wiring to the meter is
capable of handling the voltage, then there is no problem because the
I squared R voltage drop is negligible at that current. Just make
sure that the circuit is fused with low current fuses at the shunt.

The transformer solution does have the advantage of isolation, so it's
a more attractive, even tho much more expensive, solution.


--
@@[email protected]@[email protected]@@[email protected]@[email protected]@[email protected]@@[email protected]@[email protected]@[email protected]@,@@[email protected]@[email protected],@@[email protected]@[email protected]@[email protected]@
###Got a Question about ELECTRONICS? Check HERE First:###
http://users.pandora.be/educypedia/electronics/databank.htm
My email address is whitelisted. *All* email sent to it
goes directly to the trash unless you add NOSPAM in the
Subject: line with other stuff. alondra101 <at> hotmail.com
Don't be ripped off by the big book dealers. Go to the URL
that will give you a choice and save you money(up to half).
http://www.everybookstore.com You'll be glad you did!
Just when you thought you had all this figured out, the gov't
changed it: http://physics.nist.gov/cuu/Units/binary.html
@@[email protected]@[email protected]@[email protected]@[email protected]@[email protected]@[email protected]@@[email protected]@[email protected]@@[email protected]@[email protected]@[email protected]@[email protected]@[email protected]@[email protected]@@
 
F

Fred Abse

Jan 1, 1970
0
There is no such thing as a "current to voltage converter" transformer.

What you're describing is using what's called a "current transformer" and
a "burden resistor" to generate an AC voltage which is proportional to the
current flowing in the primary, which is the single wire running through
or looped through the center of the toroidal core.

Sorry, John, beg to differ here. Any transformer having current in the
primary will induce a voltage in the secondary. There is no need for a
burden resistor. OK, I know there's no such thing as an infinite impedance
measuring device, but a 200 meg input DVM is reasonable approximation, and
I've used one of those with Rogowski coils before now .......

The modern type of feedback-linearized Hall effect current converter
*does* need a burden resistor, since you're actually measuring the
feedback current.

ISTM that's as near current to voltage as dammit.
 
J

John Fields

Jan 1, 1970
0
There is no need to run currents over that distance. If the shunt is
located at the motor, then 49.999 amps go thru the shunt, and only 1
mA (assuming a 1 mA meter movement) has to travel remotely to the
meter. If the meter is insulated and the wiring to the meter is
capable of handling the voltage, then there is no problem because the
I squared R voltage drop is negligible at that current. Just make
sure that the circuit is fused with low current fuses at the shunt.

---
If a shunt is used at the motor, then the meter and the wire going to it
from the shunt will appear as three series resistors in parallel with
the shunt and the current going through the meter will be I = E/R, where
E is the voltage dropped across the shunt and R is the resistance of the
meter and the wiring connecting it to the shunt. Since the shunt will
look like a very low impedance voltage source it will only be capable of
supplying current into the meter depending on the voltage which it drops
with the motor current flowing through it.

For example, if we have a 50A 100mV shunt it will supply 1mA into
50mV/1mA = 50 ohms.

I believe most 1mA AC meters will have an internal impedance of around
1000 ohms, so that makes it a non-solution.
 
J

John Fields

Jan 1, 1970
0
Sorry, John, beg to differ here. Any transformer having current in the
primary will induce a voltage in the secondary. There is no need for a
burden resistor. OK, I know there's no such thing as an infinite impedance
measuring device, but a 200 meg input DVM is reasonable approximation, and
I've used one of those with Rogowski coils before now .......

---
I suspect that if you were to use a current transformer with an unloaded
secondary in this application you'd be in for a nasty surprise!

Let's take, for example, a current transformer with a 1000 turn
secondary and a single turn primary (an unlooped wire going through the
center of the toroid) with 50A going through it. Since the turns ratio
of the transformer is 1000, 50A flowing through the primary will try to
induce 50/1000 = 50mA in the secondary. So, since E = IR and the
unloaded secondary looks like an open circuit, the voltage induced in
the secondary will be E = IR = 0.05A*infinite ohms = infinite Volts!

Looking at it a little more realistically, with your 200 megohm load on
the secondary the voltage would only rise to 5.0E-2A * 2.0E11 ohms =
1.0E11V = 100,000,000,000V, but it might still be a good idea to load
the secondary down a little more heavily to get the voltage down to
where your meter can measure it on a more conveniently available range.
;)
 
L

Luhan Monat

Jan 1, 1970
0
John said:
Nor would it be a good idea to place the burden resistor directly across
the secondary unless the resistance of the volmeter and the run of wire
is taken into consideration.
Putting the resistor directly accross the secondary would work fine. The
wire resistance is too low to effect the voltmeter reading, and the
voltmeter's effective resistance is way to high to effect the
transformer's load.
 
J

John Fields

Jan 1, 1970
0
Putting the resistor directly accross the secondary would work fine. The
wire resistance is too low to effect the voltmeter reading, and the
voltmeter's effective resistance is way to high to effect the
transformer's load.

---
Sloppy work.

You should cite the wire size and the internal impedance of the
voltmeter before running off half-cocked. And, it's 'affect', not
'effect'.
 
L

Luhan Monat

Jan 1, 1970
0
John said:
---
Sloppy work.

You should cite the wire size and the internal impedance of the
voltmeter before running off half-cocked. And, it's 'affect', not
'effect'.

You must be using 'voltmeter' in a diffent sense than originally
proposed. I'm talking about a voltmeter as you would use as a test
instrument, not just some 'meter' that reads out in 'volts'.

Most commercial voltmeters present at least 1 megohm to the circuit they
are measuring. Hence, wire size and loading are not significant.
 
L

Luhan Monat

Jan 1, 1970
0
John said:
---
Sloppy work.

You should cite the wire size and the internal impedance of the
voltmeter before running off half-cocked. And, it's 'affect', not
'effect'.

Also, to be fair, given that you were using the other meaning of
'voltmeter', your original comment is entirely logical.
 
J

John Fields

Jan 1, 1970
0
You must be using 'voltmeter' in a diffent sense than originally
proposed. I'm talking about a voltmeter as you would use as a test
instrument, not just some 'meter' that reads out in 'volts'.

---
I think it's much more likely that a passive meter would be used as a
full-time monitor, reducing that 1 megohm considerably.
---
Most commercial voltmeters present at least 1 megohm to the circuit they
are measuring. Hence, wire size and loading are not significant.

---
Depends totally on the voltmeter, the wire size, and the current
transformer.

Take a look at a 0-5VAC iron vane panel meter (Simpson 2153) wired to a
current transformer with 24AWG wire.
 
J

John Fields

Jan 1, 1970
0
Also, to be fair, given that you were using the other meaning of
'voltmeter', your original comment is entirely logical.
 
D

Don Kelly

Jan 1, 1970
0
John Fields said:
---
If a shunt is used at the motor, then the meter and the wire going to it
from the shunt will appear as three series resistors in parallel with
the shunt and the current going through the meter will be I = E/R, where
E is the voltage dropped across the shunt and R is the resistance of the
meter and the wiring connecting it to the shunt. Since the shunt will
look like a very low impedance voltage source it will only be capable of
supplying current into the meter depending on the voltage which it drops
with the motor current flowing through it.

For example, if we have a 50A 100mV shunt it will supply 1mA into
50mV/1mA = 50 ohms.

I believe most 1mA AC meters will have an internal impedance of around
1000 ohms, so that makes it a non-solution.
----------
Sorry, I don't follow that reasoning.

A 50A, 100mV shunt will produce 100mV at 50A and have a resistance of 0.002
ohms unless it is tailor made for a specific meter as some older Weston
shunts were. As long as the meter and connecting wires have an resistance
which is orders of magnitude higher than that of the shunt, there is no
problem.
It is not designed to drive a specific current in the meter and, in fact,
the lower the meter current, the better. Use a millivoltmeter and label the
scale so 100mV =50A.
The only problem may be that a shunt is not normally used for AC but as this
appears to be for indication only, that should not be a problemWhether AC or
DC, in an industrial environment it might be a good idea to use shielded
and/or twisted leads.
 
J

John Fields

Jan 1, 1970
0
----------
Sorry, I don't follow that reasoning.

A 50A, 100mV shunt will produce 100mV at 50A and have a resistance of 0.002
ohms unless it is tailor made for a specific meter as some older Weston
shunts were. As long as the meter and connecting wires have an resistance
which is orders of magnitude higher than that of the shunt, there is no
problem.

---
Actually, there is.

A 1mA meter with an internal resistance of 1000 ohms will require 1V to
drive it to full scale, which a 100mV shunt will be unable to produce.

Watson's suggestion to use a 1mA movement, therefore, won't work unless
the meter has an internal resistance of R = E/I = 100mV/1mA = 100R.

Looking around for solutions, though, a Simpson 05400 iron vane 50mA
AC milliammeter

http://www.simpsonelectric.com/pdf/webpdfe/Round AAC.pdf

with an internal impedance of 80 ohms might work with a 20 ohm series
resistance, which could be made up by the wire run. 200' of 30AWG comes
out to about 20 ohms, but it's kind of flimsy so a better solution would
be, say, 200' of #20 (or #18, or #16...) and a 50 ohm rheostat.
---
It is not designed to drive a specific current in the meter and, in fact,
the lower the meter current, the better. Use a millivoltmeter and label the
scale so 100mV =50A.

---
The problem with going that way seems to be that there seem to be no
passive AC panel meters rated for 100mVAC full scale. At least I've had
no luck at all in finding one. I suppose putting a step-up transformer
primary across the shunt and measuring the voltage on the secondary
would work.
 
Top