I have eight 6-volt bats configured for 24 Volts. We've had 3 weeks of
absolute garbage weather and the DOD is getting to be far too high (about
70% DOD). I don't have a 24V charger, and I'm planning on moving to a 48V
configuration in the spring.
I have three 160W BP panels (24V) that with mppt pull down 17A @24V - when
the sun shines. But it hasn't for a long time. Did I say that already? ;-)
Until I get a proper charger which matches the system voltage, I was
contemplating using my 12VDC charger across a pair of bats while still
configured as-is. I would expect the power being dumped into the connected
pair to flow out and equalize into the other bats as well. Of course, at 6A
and 12V, its going to take a week to put in any appreciable amount of
power.
Anyone see a problem with the above? Without the sun? With the sun? I'd have
the inverter offline while charging..
--
Brian
(I would think that breaking the bank in 1/2 and charging 1 set while the
other stayed production would result in a very dangerous situation if I
tried to reconnect a 100% charged bank to say a 0% charged bank. Ie,
immediate FAST current flow to equalise potential. Ie explosive risk.. You'd
have to have both sets fully charged to reconnect.)
absolute garbage weather and the DOD is getting to be far too high (about
70% DOD). I don't have a 24V charger, and I'm planning on moving to a 48V
configuration in the spring.
I have three 160W BP panels (24V) that with mppt pull down 17A @24V - when
the sun shines. But it hasn't for a long time. Did I say that already? ;-)
Until I get a proper charger which matches the system voltage, I was
contemplating using my 12VDC charger across a pair of bats while still
configured as-is. I would expect the power being dumped into the connected
pair to flow out and equalize into the other bats as well. Of course, at 6A
and 12V, its going to take a week to put in any appreciable amount of
power.
Anyone see a problem with the above? Without the sun? With the sun? I'd have
the inverter offline while charging..
--
Brian
(I would think that breaking the bank in 1/2 and charging 1 set while the
other stayed production would result in a very dangerous situation if I
tried to reconnect a 100% charged bank to say a 0% charged bank. Ie,
immediate FAST current flow to equalise potential. Ie explosive risk.. You'd
have to have both sets fully charged to reconnect.)