W

Watson A.Name - \Watt Sun, the Dark Remover\

Jan 1, 1970
0
SQLit said:
answer depends on the dimmer. Some dimmers just burn off the excess voltage
as heat. Ever notice some of commercial dimmers and the huge heat sinks on
them.

Thst's not because they "burn off" the excess voltage. They still work
under the principle of delaying switching the current on for part of the
AC cycle. The reason for the large heatsinks is they are dimming large
amounts of power. In a commercial bldg, a ceiling of lights is a lot
more power than the 600W of light the usual residential dimmier is rated
for.
I will bet that if you try an 100 watt lamp and measure it at 100% and then
again at 50% your not going to see much of a difference in the usage. (ahead
of the dimmer)

See earlier followups.

[snip]
 
W

Watson A.Name - \Watt Sun, the Dark Remover\

Jan 1, 1970
0
Tim Wescott said:
Yes, your consumption goes down so your bill goes down (or should).
Unfortunately your light output goes down faster than your bill, because
light bulbs can't be efficiently dimmed.

And it should be said that incandescent lights are very inefficient to
begin with. The halogen bulbs are the most efficient of the common
incandescents, but they can't be dimmed without shortening their life.

Someone needs to point all these questions to the authoritive website
for this, Don Klipstein's lighting website.
http://members.misty.com/don/light.html
 
R

Rich Grise

Jan 1, 1970
0
I was reading some promiotional stuff on the Lumileds website. They
pointed out that the white LEDs have the advantage that they can be
dimmed, and the color temperature doesn't change, in other words they
don't have the disadvantage of incandescents that as they are dimmed,
the amount of light per watt diminishes.

LEDs for light seem to come up a lot - I very seldom see an incandescent
red stop light, for example. But are they really more efficient, like
lumens per watt, or however that's measured? 'Cause if so, it seems like
a no-brainer, although the one "white" LED flashlight I've seen was very
blue, and would have been icky for general room lights. Maybe a reading
lamp...

But do they publish that sort of thing, i.e. so many watts in -> so
many photons out, or something?

Thanks!
Rich
 
W

Watson A.Name - \Watt Sun, the Dark Remover\

Jan 1, 1970
0
Tzortzakakis Dimitrios said:
You're wrong both-sorry but that's it.A dimmer is *not* a potentiometer, so
there's no energy consumed on it.Usually it has a triac (which is a simple
power electronic device, like two thyristors in anti-parallel
connection).

A TRIAC is a thyristor, as is a SCR. In Google, type in define
thyristor and see what comes up.
 
S

Spehro Pefhany

Jan 1, 1970
0
LEDs for light seem to come up a lot - I very seldom see an incandescent
red stop light, for example. But are they really more efficient, like
lumens per watt, or however that's measured? 'Cause if so, it seems like
a no-brainer, although the one "white" LED flashlight I've seen was very
blue, and would have been icky for general room lights. Maybe a reading
lamp...

You get a lot more efficiency from LEDs making *colored* light because
they don't create white light, most of which has to be filtered out.
For white light they are currently between incandescent and
fluorescent lamps in efficiency, but MUCH more expensive for room
lighting, as I understand it.
But do they publish that sort of thing, i.e. so many watts in -> so
many photons out, or something?

Yeah, but it's pretty complicated- taking into account how much usable
light you actually get of what wavelength and how it's distributed
around the center axis etc.. including physiological factors, of
course. I think John Fields knows a fair bit about this.
Thanks!
Rich


Best regards,
Spehro Pefhany
 
W

Watson A.Name - \Watt Sun, the Dark Remover\

Jan 1, 1970
0
Rich Grise said:
LEDs for light seem to come up a lot - I very seldom see an incandescent
red stop light, for example. But are they really more efficient, like
lumens per watt, or however that's measured? 'Cause if so, it seems like
a no-brainer, although the one "white" LED flashlight I've seen was very
blue, and would have been icky for general room lights. Maybe a reading
lamp...

But do they publish that sort of thing, i.e. so many watts in -> so
many photons out, or something?

Follow the other followups. Don Klipstein's LED pages and his posts.
 
D

Dave Platt

Jan 1, 1970
0
LEDs for light seem to come up a lot - I very seldom see an incandescent
red stop light, for example. But are they really more efficient, like
lumens per watt, or however that's measured?

One figure I've seen (in a manufacturer's ad) cited an 80% reduction
in electricity use in stoplight applications.

The power saving seems to be one big motivation for switching
stoplights over to LEDs. Reduction in the number of person-hours to
do bulb replacement seems to be the other.

Here in the Silicon Valley, almost all of the stoplights seem to have
been completely converted over... all three colors are now LED-based.

'Cause if so, it seems like
a no-brainer, although the one "white" LED flashlight I've seen was very
blue,

Some are bluer, some are more white... depends on the manufacturer,
phosphor, etc. The better ones seem to be roughly comparable to a
"cool white" fluorescent tube.
and would have been icky for general room lights. Maybe a reading
lamp...

I'd be tempted to see how well one might do, in terms of color
temperature, with a set of "white" LEDs, plus a few ultrabright red or
red/orange to warm up the spectrum.
But do they publish that sort of thing, i.e. so many watts in -> so
many photons out, or something?

I believe so. Most high-brightness LEDs seem to be spec'ed in terms
of candellas of brightness, over a specific angular range, at a given
current, with a specified forward voltage.
 
| You're wrong both-sorry but that's it.A dimmer is *not* a potentiometer, so
| there's no energy consumed on it.Usually it has a triac (which is a simple
| power electronic device, like two thyristors in anti-parallel connection).

There is SOME energy consumed there. They do get hot (some get very hot).
Certainly less than a potentiometer (unless something has gone wrong), but
the consumptions not zero.
 
| The illumination output of a standard light bulb varies approximately by the
| square of the applied power. Cut the power in half and you get about one
| fourth the lumens. That is only approximate and varies somewhat with the
| type of filament.

Assuming a constant filament. If you get a lower wattage filament,
then you save power, lower cost, and have proportionally less light.
But one factor to consider is the human sensitivity and perception
of light. And that's non-linear.
 
| And, as an additional issue, it's generally a bad idea to use a dimmer
| with quartz-halogen lamps. When dimmed, the bulbs run a good deal
| cooler, the halogen-sequestering-and-redeposition of the tungsten
| doesn't work as well, the tungsten tends to plate out on the inside of
| the tube and dim the bulb, and the bulb lifetime is greatly decreased.

And this is a frequent problem with those torchiere floor lamps which
usually have a dimmer and a 300 (more than you need most of the time)
watt QH bulb. So people dim them, usually. Unfortunately, getting a
lower wattage bulb is more expensive, if they can even be found in the
same size.


| All in all, as others have said, it makes more economic sense to use
| smaller bulbs at full power rather than dimming a high-wattage bulb.

Agreed. Getting variability should be done in the form of turning more
or fewer bulbs on. A lamp with 8 small 40 watt QH bulbs and a switch
to control how many are on would be nice ... and expensive.
 
| This in particular is why you shouldn't use dimmers with lamps that are
| mounted so that the filament is above the socket. When such lamps burn
| out it is not uncommon for a broken piece of filament to fall and
| briefly short across the two thick wires that feed the ends of the filament.

I had one bulb do that in a non-brief way, once. The filament shorted
in such a way that it had about 75% if it's length still working. It
got brighter (in theory, from 60 watts to 80 watts if that estimate of
filament length was correct. The nice thing was the light now looked
a lot more "white". Unfortunately it gave out about a week later.

Someone once suggested getting 100 volt (because that is their nominal
voltage) light bulbs intended for the Japanese domestic market. That
would get a brighter whiter light. Just be sure to get a lot of them
as you will be changing bulbs more frequently. A 60 watt 100 volt bulb
run on 120 volts will be dissipating about 86 watts (NOT figuring in the
change of resistance due to the change of heat). Which could be used in
place of a 100 watt bulb. Power usage goes up. Light output goes up even
more. Bulb replacement goes up, too.

Other people prefer bulbs rated for 130 volts so they don't have to change
them so often. In hard to reach places that's definitely a plus.
 
| A few bulbs benefit from "soft starting", many and probably most do not.
| Most (but not all) bulbs have zero or negligible fatigue damage to the
| filament from a "cold start" despite a cold start jolting the filament to
| cause a "ping" sound that is audible at close range.

I've found that this can be a benefit for the small candelabra style bulbs
often used in small home chandeliers. Their filaments are constructed
in a different way with typically 4 vertical segments. I've had these
blow very often with full starting, and noticeably less often starting
dimmed. Regular bulbs haven't noticed a change.


| There is a usual prelude-to-failure uneven evaporation of the filament.
| That process causes a "thin spot" that is subject to a temperature
| overshoot during a cold start. In most lightbulbs, such a "deadly thin
| spot" is a deterioration mode of the filament that accelerates at a rate
| worse than exponentially (during operation) once it becomes significant.
| This means that for most lightbulbs, when they become unable to survive a
| cold start their operating hours are numbered. And for most (but not all)
| lightbulbs, cold starts do zero to usually-negligible damage until the
| filament has aged enough for a cold start to be fatal.

[...]

| True, but they usually don't blow out immediately unless the overload is
| very severe. Mild to moderate overload merely shortens their life.

I have seen at times some strange bulb behaviour. And this without any
dimmer involved. The bulbs sometimes start to hum. Or maybe they will
modulate the light output around 10 Hz. In these cases I have learned
they are "dead already". If others are around I'll just say "that bulb
just burned out" to which they reply "but it's still giving out light".
Then my reply is "when have you ever seen a light bulb just stop giving
out light while its on" (it happens, but it's rare enough most people
don't remember ever seeing it). I insist that it is already dead and
add that it won't come back on when the light is turned off then back
on. Often times someone is willing to actually try the switch and every
time I've been proved right. Then they start wondering about me.


| Current surge from burnout is often worse than the current surge of a
| cold start. Often when the filament breaks, an arc forms across the gap.
| The arc can be encouraged by the voltage gradient across the filament to
| expand and go across the ends of the filament, in which case the filament
| is no longer limiting current through the arc. This is what causes the
| "bright blue flash" that sometimes occurs during a burnout, especially a
| burnout during a cold start (when the filament resistance is less and
| allows more current to flow through the arc which makes the arc hotter and
| more conductive).
| Most lightbulbs have fusible links in one of their internal lead-in
| wires so that a "burnout arc" does not pop a breaker or blow a fuse.
| However, this may be inadequate for protection of dimmers.

I've had a few cases where the surge that resulted for a burn out arc
has caused other bulbs in the same fixture to burn out. In one case, all
5 bulbs in a fixture blew at the same time. In that case, all 5 bulbs
also showed multiple filament breakage, and arc damage in the base, such
as melting through the base. In another case, the bulb became welded to
the base. In another case, there was damage in the wiring itself. Two
case tripped breakers (multiple bulb burnouts in these, too).


| I believe probably true. It gets more uncertain when you have a 600
| watt or 540 watt load on a 600 watt dimmer, and it gets worse when you put
| more than one dimmer in the same box since each one adds heat to the
| others (despite the loss in each dimmer being only a few watts).

Just put a 7 watt light bulb in a small metal case and leave it one for a
while. Without good thermal dissipation, heat rise can be significant.
Many a fire has happened from decorative items with even small bulbs used
inside (such a Christmas light items).
 
| Say for instance you had four 25 watt bulbs and you needed only 25 watts
| of light. Well, you switch on only one. and you get 25 watts of light
| and pay for 25 watts of power. But if you dim your 100W lamp to get 25
| watts of light, then you might be paying for 50 watts of power. You get
| less light per watt when it is dimmed.

The 100 watt bulb in this condition has a lower color temperature. This
results in far more infrared output relative to light output compared to
normal operation. It's that "orange look".
 
| LEDs for light seem to come up a lot - I very seldom see an incandescent
| red stop light, for example. But are they really more efficient, like
| lumens per watt, or however that's measured? 'Cause if so, it seems like
| a no-brainer, although the one "white" LED flashlight I've seen was very
| blue, and would have been icky for general room lights. Maybe a reading
| lamp...

"white" LEDs are more like fluorescent lights. They are a blue LED with
some kind of phosphors for other colors.

I've seen a light with multiple LEDs in various colors, with separate
dimmers for each color. Choose your own color. It was expensive.
 
S

someone

Jan 1, 1970
0
In alt.engineering.electrical Tzortzakakis Dimitrios
| You're wrong both-sorry but that's it.A dimmer is *not* a potentiometer, so
| there's no energy consumed on it.Usually it has a triac (which is a simple
| power electronic device, like two thyristors in anti-parallel connection).

There is SOME energy consumed there. They do get hot (some get very hot).
Certainly less than a potentiometer (unless something has gone wrong), but
the consumptions not zero.

Relatively small. I would expect it would be something like a normal NP
junction where the voltage drop is about 0.6 volts. Assume a 50 watt load
using about a half ampere current. = about 0.3 watts. Other components in
the circuit may have more disappation than that.
 
S

Sylvia Else

Jan 1, 1970
0
| This in particular is why you shouldn't use dimmers with lamps that are
| mounted so that the filament is above the socket. When such lamps burn
| out it is not uncommon for a broken piece of filament to fall and
| briefly short across the two thick wires that feed the ends of the filament.

I had one bulb do that in a non-brief way, once. The filament shorted
in such a way that it had about 75% if it's length still working. It
got brighter (in theory, from 60 watts to 80 watts if that estimate of
filament length was correct. The nice thing was the light now looked
a lot more "white". Unfortunately it gave out about a week later.

Someone once suggested getting 100 volt (because that is their nominal
voltage) light bulbs intended for the Japanese domestic market. That
would get a brighter whiter light. Just be sure to get a lot of them
as you will be changing bulbs more frequently. A 60 watt 100 volt bulb
run on 120 volts will be dissipating about 86 watts (NOT figuring in the
change of resistance due to the change of heat). Which could be used in
place of a 100 watt bulb. Power usage goes up. Light output goes up even
more. Bulb replacement goes up, too.

Other people prefer bulbs rated for 130 volts so they don't have to change
them so often. In hard to reach places that's definitely a plus.

There was some correspondence in New Scientists about the impact of
mains overvoltages on the life of incandescent lamps. Something along
the lines of a 10% overvoltage halves the life.

It's just possible that the lamp manufacturers really have chosen an
operating point that represents the best choice for the majority of people.

I use flourescent substitutes in some places, but they're not exactly a
perfect solution either. The ones I use take a significant time
(minutes, I think) to reach their peak brightness, an effect that seems
to get worse as they age. However I've yet to have to replace one.

I don't know that you can use a dimmer with them, though. I rather
suspect they wouldn't like that.

Sylvia.
 
| Relatively small. I would expect it would be something like a normal NP
| junction where the voltage drop is about 0.6 volts. Assume a 50 watt load
| using about a half ampere current. = about 0.3 watts. Other components in
| the circuit may have more disappation than that.

Put a small wattage light in the same kind of enclosure. Experiment until
you find the wattage that gives the same temperature rise over a long
settling time. Then you'll have an estimate of the waste by the device.
 
| I use flourescent substitutes in some places, but they're not exactly a
| perfect solution either. The ones I use take a significant time
| (minutes, I think) to reach their peak brightness, an effect that seems
| to get worse as they age. However I've yet to have to replace one.
|
| I don't know that you can use a dimmer with them, though. I rather
| suspect they wouldn't like that.

There are dimmable ballasts. That obviously combines the role of limiting
the current and adjusting the current. I bet they are all solid-state.
 
R

Roger Johansson

Jan 1, 1970
0
Sylvia Else said:
I use flourescent substitutes in some places, but they're not exactly a
perfect solution either. The ones I use take a significant time
(minutes, I think) to reach their peak brightness, an effect that seems
to get worse as they age. However I've yet to have to replace one.

I don't know that you can use a dimmer with them, though. I rather
suspect they wouldn't like that.

Here is a nice collection of articles about dimming fluoros:

http://members.misty.com/don/f-dim.html
 
D

Don Klipstein

Jan 1, 1970
0
LEDs for light seem to come up a lot - I very seldom see an incandescent
red stop light, for example. But are they really more efficient, like
lumens per watt, or however that's measured? 'Cause if so, it seems like
a no-brainer, although the one "white" LED flashlight I've seen was very
blue, and would have been icky for general room lights. Maybe a reading
lamp...

LEDs are now getting more efficient than incandescent lamps, but there
are extra factors in traffic lights, flashlights, and some other
applications.

Traffic lights: The incandescents in those are not regular ones, but
ones designed to last (typically) 8,000 hours. These are something like
30% less efficient than the usual household incandescents.
But the real kicker is that a red filter or a green filter blocks about
2/3, maybe about 70% of the light. You probably get only 3-4 lumens out
per watt in, as opposed to around 11-17 lumens per watt with the usual
"standard" household incandescents. (Slightly less for 230V versions in
part because their filaments are thinner and have to be run slightly
cooler for the same life expectancy).
But they make red LEDs and trafic signal green LEDs with about the same
overall luminous efficacy as white LEDs - 20 lumens per watt, even more.
Lumileds makes some red ones that get 40 and traffic signal green ones
that get 30 or more. Nichia makes traffic signal green LEDs that get 25
lumens/watt. Similarly efficient ones are available from ETG.

Flashlights: The main problem with incandescent is that their efficiency
decreases greatly as the battery weakens. On the other hand, white LEDs
usually have slightly increased efficiency when moderately underpowered.
Their efficiency is usually maximized with current somewhere around 20% of
the "typical" current in the datasheet, and as current decreases below
that they lose efficiency but not nearly as rapidly as incandescents do.

I mention more in http://www.misty.com/~don/lede.html

BTW - Many LEDs actually have some color change as current is varied.

- Don lipstein ([email protected])
 