Optics ain't my strong suit. I freely admit that. However, I have a 1000
square foot single story steel shed I am lighting from photovoltaics and
batteries/inverter. For a given amount of illumination per square squird of
floor area, what is the most economical and efficient method of lighting?
Plain old fluorescent fixtures? Compact fluorescent bulbs? Some other
(relatively inexpensive) technology I'm not aware of? Are all fluorescent
fixtures the same efficiency or are some designs/brands better than others?
Same with compact fluorescents?

I'd rather spend a little money to make the lighting efficient so that I can
run the spectrum analyzer and sig gen a little longer from available power
sources.

Jim
 
J

Joerg

Jan 1, 1970
0
Hello Jim,

Optics ain't my strong suit. I freely admit that. However, I have a 1000
square foot single story steel shed I am lighting from photovoltaics and
batteries/inverter. For a given amount of illumination per square squird of
floor area, what is the most economical and efficient method of lighting?
Plain old fluorescent fixtures? Compact fluorescent bulbs? Some other
(relatively inexpensive) technology I'm not aware of? Are all fluorescent
fixtures the same efficiency or are some designs/brands better than others?
Same with compact fluorescents?

I'd rather spend a little money to make the lighting efficient so that I can
run the spectrum analyzer and sig gen a little longer from available power
sources.

I recently converted much here to CFL after I found some that worked
well and were cheap. Costco had a sweet deal (maybe still does) where
utility subsidies brought the cost of 23W and 14W versions down to
around a Dollar a piece. If you have a good reflector behind them they
are really bright, especially the 23W versions which are claimed to
produce the output of a 100W incandescent bulb (looks like they really
do now). But mind that they produce EMI. Mostly conducted which you can
muffle but also radiated which can't easily be filtered unless you place
a mesh across the face. That mesh will be a dirt and spider web
collector and can become a hazard.

AFAIK you can eke out a wee bit more efficiency if you build your own
inverters and then use larger fluorescent tubes. Plenty of circuits on
the web.

When it gets cold fluorescents need a long time to reach their target
output. Meaning more than just a few minutes. When it gets really hot I
had some of the industrial long tubes cycle off.
 
R

Rich Grise

Jan 1, 1970
0
Optics ain't my strong suit. I freely admit that. However, I have a 1000
square foot single story steel shed I am lighting from photovoltaics and
batteries/inverter. For a given amount of illumination per square squird of
floor area, what is the most economical and efficient method of lighting?
Plain old fluorescent fixtures? Compact fluorescent bulbs? Some other
(relatively inexpensive) technology I'm not aware of? Are all fluorescent
fixtures the same efficiency or are some designs/brands better than others?
Same with compact fluorescents?

I'd rather spend a little money to make the lighting efficient so that I can
run the spectrum analyzer and sig gen a little longer from available power
sources.

Put in some windows? Maybe skylights? :)

Good Luck!
Rich
 
H

Homer J Simpson

Jan 1, 1970
0
Optics ain't my strong suit. I freely admit that. However, I have a 1000
square foot single story steel shed I am lighting from photovoltaics and
batteries/inverter. For a given amount of illumination per square squird
of floor area, what is the most economical and efficient method of
lighting?

For battery operation I'd sure be looking at compact fluorescent bulbs. El
cheapo ones have crappy phosphors but I got some 15 watt for $1 ea at the
local grocery store that are really high output.
 
G

GregS

Jan 1, 1970
0
Optics ain't my strong suit. I freely admit that. However, I have a 1000
square foot single story steel shed I am lighting from photovoltaics and
batteries/inverter. For a given amount of illumination per square squird of
floor area, what is the most economical and efficient method of lighting?
Plain old fluorescent fixtures? Compact fluorescent bulbs? Some other
(relatively inexpensive) technology I'm not aware of? Are all fluorescent
fixtures the same efficiency or are some designs/brands better than others?
Same with compact fluorescents?

I'd rather spend a little money to make the lighting efficient so that I can
run the spectrum analyzer and sig gen a little longer from available power
sources.

Its obviously efficient to use as little light as possible, in small areas.
That said, the compact florescents are pretty good but their light output
is not going to equal a 4 foot fluorescent

I just installed lights in my garage and used 10 4 foot bulbs, 3300 Lumens
each at 40 watt each. I wasn't worring about efficiency, just light output.
I must examine some lamps installed above my head. The are very much brighter
than the other fluorescents around here. I wonder what the Lumens rating is?
Well I just found out. Its less than I expected, but interesting. The GE Ecolux
is a 32 watt and outputs 3000 Lumens. Its still looks
superbright to me SPX41.


greg
 
H

Homer J Simpson

Jan 1, 1970
0
I must examine some lamps installed above my head. The are very much
brighter
than the other fluorescents around here. I wonder what the Lumens rating
is?
Well I just found out. Its less than I expected, but interesting. The GE
Ecolux
is a 32 watt and outputs 3000 Lumens. Its still looks
superbright to me SPX41.

It's all in the phosphors.
 
P

Paul Hovnanian P.E.

Jan 1, 1970
0
RST Engineering (jw) said:
Optics ain't my strong suit. I freely admit that. However, I have a 1000
square foot single story steel shed I am lighting from photovoltaics and
batteries/inverter. For a given amount of illumination per square squird of
floor area, what is the most economical and efficient method of lighting?
Plain old fluorescent fixtures? Compact fluorescent bulbs? Some other
(relatively inexpensive) technology I'm not aware of? Are all fluorescent
fixtures the same efficiency or are some designs/brands better than others?
Same with compact fluorescents?

I'd rather spend a little money to make the lighting efficient so that I can
run the spectrum analyzer and sig gen a little longer from available power
sources.

Jim

You might want to ask this question over on sci.engr.lighting

If they are still speaking to us, that is. ;-)

You might also want to give a few more details about what sort of
lighting levels (or what kind of tasks will be performed) in this
structure. Efficiency might be a factor of lighting levels, CRI, etc.
 
V

Victor Roberts

Jan 1, 1970
0
You might want to ask this question over on sci.engr.lighting

If they are still speaking to us, that is. ;-)

You might also want to give a few more details about what sort of
lighting levels (or what kind of tasks will be performed) in this
structure. Efficiency might be a factor of lighting levels, CRI, etc.

Since we don't have the details that Paul has mentioned, I'm
going to go out on a limb and generalize here.

For general lighting it's hard to beat the efficacy of high
quality 4-foot T8 (1 inch diameter) fluorescent lamps on
quality electronic ballasts and mounted in high performance
fixtures. Compact fluorescent lamps are less efficient than
linear fluorescent lamps. Incandescent lamps are much less
efficient. Metal halide lamps come close, but their have
terrible lumen depreciation so their mean efficacy over life
is worse than fluorescent lamps.

My generalization falls apart if your application does not
need uniform light levels. If you can use task lighting in
critical areas and lower light levels in other areas then
there may be better solutions.

All linear fluorescent lamps are not equal and all ballasts
and fixtures are not equal. The lap data provided by the
"big three" can generally be assumed to be accurate so you
can compare different T8 lamps so discover their minor
differences.

Some people prefer T5 linear lamps, but they are no more
efficient than T8 lamps of the same length when both are
operated on electronic ballasts.

If you are operating from DC power I would suggest
purchasing ballasts designed to operate from your DC power
source instead of using AC ballasts and a DC-to-AC
converter, which will only waste power.

I'm sure you will get other opinions.

--
Vic Roberts
http://www.RobertsResearchInc.com
To reply via e-mail:
replace xxx with vdr in the Reply to: address
or use e-mail address listed at the Web site.

This information is provided for educational purposes only.
It may not be used in any publication or posted on any Web
site without written permission.
 
J

JohnR66

Jan 1, 1970
0
Paul Hovnanian P.E. said:
You might want to ask this question over on sci.engr.lighting

If they are still speaking to us, that is. ;-)

You might also want to give a few more details about what sort of
lighting levels (or what kind of tasks will be performed) in this
structure. Efficiency might be a factor of lighting levels, CRI, etc.

It would be necessary to know the available power to give you a good answer.
Fluorescent is the way to go, but you could limited to single 9 watt lamp to
several multi tube 4' fixtures depending on available power and required
runtime.
John
 
R

RST Engineering \(jw\)

Jan 1, 1970
0
Thanks for all the answers, and more thanks for all the questions. The
"metal building" in question is an aircraft hangar that doubles as my
airport electronics lab. I use the lab to validate and true up designs done
for both my manufacturing company (www.rstengineering.com) and my monthly
magazine column designs (www.kitplanes.com).

The lighting will be used for maintenance on the aircraft and general hangar
lighting for the machine shop, the parts bins, and the like. Each
electronics bench has its own individual two-tube fluorescent fixture that
gives me very good lighting on a microscopic scale.

As to "how much power is available", the answer is that I've got a 3 kW
gasoline generator that kicks in when the voltage drops below a critical
level on the 12 volt batteries being charged by the solar panels. The
answer is that I'm limited to something below 3 kW over the long haul, but
could give you 5 kW on a short term basis.

Now, since the consensus seems to be that a fluorescent fixture with 4'
bulbs is the most efficient, how do you select the fixture. I understand
that the bulbs themselves have a lumen/watt rating on them, but how do you
determine the efficiency of the ballast/fixture itself?

Jim
 
R

Richard

Jan 1, 1970
0
Just pick up a two bulb fixture with a large reflector and an electronic
ballast and then pick up a pair of 25 watt bulbs in place of typical 32 watt
bulbs. If you are going with 2 two bulb fixtures better to get a 4 bulb
ballast and wire the two fixtures together with that one ballast rather than
use two ballasts. You might even consicer single bulb fixtures if you can
find them with a large reflector and use a two or four bulb ballist and up
to four fixtures connected together. There are even 17 watt bulbs out there
if you can find them.

Richard.
 
J

JohnR66

Jan 1, 1970
0
Richard said:
Just pick up a two bulb fixture with a large reflector and an electronic
ballast and then pick up a pair of 25 watt bulbs in place of typical 32
watt bulbs. If you are going with 2 two bulb fixtures better to get a 4
bulb ballast and wire the two fixtures together with that one ballast
rather than use two ballasts. You might even consicer single bulb fixtures
if you can find them with a large reflector and use a two or four bulb
ballist and up to four fixtures connected together. There are even 17 watt
bulbs out there if you can find them.

Richard.
NOT recommended. You just can't install any wattage fluorescent tube in any
fixture even if it fits. The voltage and current characteristics of the
ballast is designed for a particular bulb.
John
 
J

JohnR66

Jan 1, 1970
0
RST Engineering (jw) said:
Thanks for all the answers, and more thanks for all the questions. The
"metal building" in question is an aircraft hangar that doubles as my
airport electronics lab. I use the lab to validate and true up designs
done for both my manufacturing company (www.rstengineering.com) and my
monthly magazine column designs (www.kitplanes.com).

The lighting will be used for maintenance on the aircraft and general
hangar lighting for the machine shop, the parts bins, and the like. Each
electronics bench has its own individual two-tube fluorescent fixture that
gives me very good lighting on a microscopic scale.

As to "how much power is available", the answer is that I've got a 3 kW
gasoline generator that kicks in when the voltage drops below a critical
level on the 12 volt batteries being charged by the solar panels. The
answer is that I'm limited to something below 3 kW over the long haul, but
could give you 5 kW on a short term basis.

Now, since the consensus seems to be that a fluorescent fixture with 4'
bulbs is the most efficient, how do you select the fixture. I understand
that the bulbs themselves have a lumen/watt rating on them, but how do you
determine the efficiency of the ballast/fixture itself?

Jim
When speaking of available power. How much is available for lighting? Lets
say you supply 3 kw continuous. What is the maximum load your equipment puts
on the supply. Subtract that from the total and this is what is left for
lighting. Wouldn't hurt to give it a 20% cushion.
You probably should have an electronic engineer evaluate your situation. You
might have to deal with power factor correction to get the best out of your
system.

Electronic ballasts will give an edge in efficiency. If the building is
close to a square in shape, I can see four 8' tube fixtures (two bulbs per
fixture) in two rows across the ceiling if it is sufficiently high. It would
use under 1 kw.

John
 
T

TKM

Jan 1, 1970
0
JohnR66 said:
NOT recommended. You just can't install any wattage fluorescent tube in
any fixture even if it fits. The voltage and current characteristics of
the ballast is designed for a particular bulb.
John

Agree. If the lamp type is listed on the ballast label, then that lamp is
O.K. to use. If the lamp is not listed, check the ballast manufacturer's
web site and the ballast listing. The ballast manufacturer wants to make
that ballast as widely used as possible, so if the lamp is not listed for
use on a particular ballast, there is a reason.

Terry McGowan
 
V

Victor Roberts

Jan 1, 1970
0
Now, since the consensus seems to be that a fluorescent fixture with 4'
bulbs is the most efficient, how do you select the fixture. I understand
that the bulbs themselves have a lumen/watt rating on them, but how do you
determine the efficiency of the ballast/fixture itself?

8-foot fluorescent lamps are slightly more efficient than
4-foot lamps of the same type. I suggested 4-foot lamps
because they are almost as efficient as 8-foot lamps, are
much more convenient, are available in a greater variety of
types and colors and may be less expensive.

To find the most efficient ballast you will need information
that is available on the ballast data sheet and may also be
printed on the ballast labels. To compare the efficiency of
various ballasts for the same type and number of lamps,
compute the Ballast Efficiency Factor (BEF). The BEF is the
Ballast Factor (BF) divided by the ballast input power. You
can only compare the BEF for ballasts designed to operate
the SAME TYPE AND NUMBER OF LAMPS. Also, if any ballast
under consideration operates more than one type of lamp,
remember to use the BF and input power for the same type and
number of lamps when you compare ballasts.

If you decided to use a DC-input ballast, as I suggested to
eliminate the additional losses of an DC-to-AC converter,
then your ballast choices will be limited.

I normally don't work with fixtures, but you can also find
fixture efficiency data on fixture data sheets. I would not
choose 'any" fixture, as has been suggested.

--
Vic Roberts
http://www.RobertsResearchInc.com
To reply via e-mail:
replace xxx with vdr in the Reply to: address
or use e-mail address listed at the Web site.

This information is provided for educational purposes only.
It may not be used in any publication or posted on any Web
site without written permission.
 
V

Victor Roberts

Jan 1, 1970
0
Just pick up a two bulb fixture with a large reflector and an electronic
ballast and then pick up a pair of 25 watt bulbs in place of typical 32 watt
bulbs. If you are going with 2 two bulb fixtures better to get a 4 bulb
ballast and wire the two fixtures together with that one ballast rather than
use two ballasts. You might even consicer single bulb fixtures if you can
find them with a large reflector and use a two or four bulb ballist and up
to four fixtures connected together. There are even 17 watt bulbs out there
if you can find them.

25-watt lamps will reduce power consumption, but will also
reduce light levels. For a new installation designed for a
specific light level it is not clear that 25-watt lamps
provide either the most efficient or most economical
solution.

--
Vic Roberts
http://www.RobertsResearchInc.com
To reply via e-mail:
replace xxx with vdr in the Reply to: address
or use e-mail address listed at the Web site.

This information is provided for educational purposes only.
It may not be used in any publication or posted on any Web
site without written permission.
 
D

Don Klipstein

Jan 1, 1970
0
El cheapo ones have crappy phosphors but I got some 15 watt for $1 ea at
the local grocery store that are really high output.

My experience is that in compact fluorescents, lousy phosphors are only
or almost only used in ones available at dollar stores, or of brands
usually found at dollar stores.

- Don Klipstein ([email protected])
 
D

Dirk Bruere at NeoPax

Jan 1, 1970
0
GregS said:
I just installed lights in my garage and used 10 4 foot bulbs, 3300 Lumens
each at 40 watt each. I wasn't worring about efficiency, just light output.
I must examine some lamps installed above my head. The are very much brighter
than the other fluorescents around here. I wonder what the Lumens rating is?
Well I just found out. Its less than I expected, but interesting. The GE Ecolux
is a 32 watt and outputs 3000 Lumens. Its still looks
superbright to me SPX41.

That's about 100 lumens per watt.
The best white light LEDs can do about half that, which is worth
considering for small lights eg bench spotlights etc.
 
R

RickR

Jan 1, 1970
0
We should keep in mind just how much difference there is between some
of these options. In many cases we could be talking about fractions of
a percent, that could be easily overwhelmed by other factors.

Assuming that $$ are not unlimited you may soon find a region of
vanishing returns.

It is not well understood by the general public how the temp of the
bulb wall effects output and therefore efficiency. In a metal walled
structure I would look *very* closely at that.

For maximum efficiency you must start with how the light is distributed
over the area of interest. Then (for fluorescent) the lamp and ballast
as a pair! Then move to the fixture construction.

Furthermore you are using a 12VDC source and the options in ballast are
quite limited.

Richard Reid, LC
Luminous Views
 