Garage door open switch to Honeywell thermostat

DRW

Dec 21, 2011
3
Joined
Dec 21, 2011
Messages
3
I live in Minnesota and have a gas garage heater that is controlled with a simple digital Honeywell thermostat. I keep it at 40 degrees which is as low as it goes just to keep things in the garage from freezing. Twice now (in 3 years) I have left the garage door open and the heater has run all night. I'm thinking of wiring a reed switch to the garage door and to the 24v? furnace on wire of the thermostat so that the heater will not run if the garage door is not closed.

Initially, I was thinking I needed a relay but now I'm wondering if I can run the 24v from the thermostat directly through the reed switch and then to the heater.

I'm just looking for any advice or warnings I'm not considering on why I might not want to do this.

Thanks in advance
 

jackorocko

Apr 4, 2010
1,284
Joined
Apr 4, 2010
Messages
1,284
All you need to do is open circuit the thermostat control to the heater, but what exactly do you plan to use on the garage door to open circuit the thermostat control? ARe you planning on using an electrical signal or a mechanical switch to control that?

What is a reed switch?

edit: After looking up what a reed switch is, I assume you plan on using one in series with the 24V thermostat signal to the heater and using a physical magnet on the door and locate the reed switch appropriately? If so I don't see why this wouldn't work. Use a NO reed switch.
 
Last edited:

duke37

Jan 9, 2011
5,364
Joined
Jan 9, 2011
Messages
5,364
Welcome to the forum.

Reed switches are somewhat delicate, I would think it better to use a microswitch. The standard switch can manage 5A at 250V AC.
 

DRW

Dec 21, 2011
3
Joined
Dec 21, 2011
Messages
3
Thanks

Thanks for the reply. Yes, I was just going to mount the magnet on the door and the wall so that it would make contact when the door closed. I was just going to run the 24V on signal through this switch in series.
 

Resqueline

Jul 31, 2009
2,848
Joined
Jul 31, 2009
Messages
2,848
Try to estimate the current going through the thermostat circuit. If it's 100mA or less you could use a reed switch, if above then a microswitch would be more durable.
 

KMoffett

Jan 21, 2009
723
Joined
Jan 21, 2009
Messages
723
How important is it to keep the garage interior from freezing? As an alternative, you might consider (ONLY IF THERE ARE MULTIPLE FUNCTIONING OBSTRUCTION SAFETY SWITCHES) an automatic, timed door-closer. A reed or microswitch indicates door is opened and starts timer. At the end of the time, the timer trips the door-operate switch and closes the door.

Ken
 
Last edited:

DRW

Dec 21, 2011
3
Joined
Dec 21, 2011
Messages
3
I'll look around for different types of switches, a mechanical micro switch may be the easiest choice. Looks like a lot of the magnetic switches are 12V, I'm assuming I would need a relay and a 12V power supply. I like the idea of it automatically closing the door but I am wanting to keep it as simple as possible and my primary concern is that the heater doesn't run all night.
 