Help hooking a Power line EMI filter to my 2hp Teco VFD 220 volt ac

sea

Mar 28, 2012
30
Joined
Mar 28, 2012
Messages
30
Just making sure I hook this up right, im using 220 ac volts .. two power one ground from my main panel in my shop

I assume P and N are the positive line in's from the my main feed line/panel and E is the earth ground from same ?

Are P1 .. N1 and E the lines that then go into power my VFD drive ?

emi filter.jpg
 

Minder

Apr 24, 2015
3,478
Joined
Apr 24, 2015
Messages
3,478
That is correct.
BTW, I prefer to spend money on the other end, IOW a 3 ph choke between the output and the motor, especially if it is an older, non-vector rated motor.
M.
 
  • Like
Reactions: sea

sea

Mar 28, 2012
30
Joined
Mar 28, 2012
Messages
30
Its actually a brand new Leeson motor rated for VFD .. I got Lutz Drive flex wire for that end, thought id also throw some ferrite chokes on the leads coming out of VFD that go to motor side
Your thoughts?
Thanks for you answer on the above, thats awesome
 

Minder

Apr 24, 2015
3,478
Joined
Apr 24, 2015
Messages
3,478
The most efficient is the 3ph choke intended for the purpose.
On the input side, the first thing in line is a 3ph rectifier and a large bank of electrolytic capacitors, so the input is pretty well damped at that point.
M.
 