I need help (KVA)

G

george

Jan 1, 1970
0
Hi,

I would like to know the Kva for the following appliances.

4 freezers at 5 amps each

3 chiller units at 3 amps each

2 chillers at 35 amps each.

I do not know if they are resistive or conductive(if that is necessary
for the answer)

Would the answer be 79 * 240 /1000 = 18.96??

Hope you can help.

Confused
 
G

GotCoffee

Jan 1, 1970
0
If all you appliances are running off of 240 you're almost correct...
you for got to add in the 4 freezers so add 20 more amps and you should
come up with 23.76kVA
 
D

Don Kelly

Jan 1, 1970
0
GotCoffee said:
If all you appliances are running off of 240 you're almost correct...
you for got to add in the 4 freezers so add 20 more amps and you should
come up with 23.76kVA

That is an upper limit - assuming all are running at the currents given and
all are at the same power factor.[/QUOTE]
 