KJD series switches.

boyd

Oct 7, 2016
64
Joined
Oct 7, 2016
Messages
64
I have posted a couple of times before with this project. Attached is a very simple circuit of how I plan to control my 2.2kw dust extractors with just turning on the machine. There is a whole lot more I am going to add into the system.

I found the cheapest way was to buy US$1.70 230vac to 12vdc power supplies and install them into each machine. This will give me a 12vdc output once a machine is switched on.

What I have done though is use a single solid state relay to switch on the extractors whereas the KJD series of switches are double pole with built-in under current/voltage protection. I will be adding in those along with a couple of other sensors.

If anyone was interested, I would really be interested in feedback as to whether this will be fine to go or I need to have double pole relays to switch the extractors on and off or can I just do it with the phase hooked up to the relay on a single wire to on/off?

Also I am looking at a way to cheaply put in a 30 second delay before the extractor switches off along with the current/voltage protection. I have found these to put in the low voltage side:

https://www.aliexpress.com/item/1pc.../1100514896.html?spm=2114.13010608.0.0.sw6L0g

Now I just need to find current/voltage protection.

But I am VERY keen to hear from anyone more qualified than I if I have missed something?

Regards Boyd
 

Attachments

  • Visio-Automated Extractor on-off.pdf
    26 KB · Views: 75

dorke

Jun 20, 2015
2,342
Joined
Jun 20, 2015
Messages
2,342
I would say that for safety reason alone you should
use a double pole relay to switch both Phase and Neutral.

Could you please explain the need for this arrangement?

Notice that the "12V P.S." will "indicate" a working M1 machine,
while M1 may not work at all due to a malfunction in M1.

What kind of machine is M1?
 

Bluejets

Oct 5, 2014
6,901
Joined
Oct 5, 2014
Messages
6,901
Maybe I read it wrong but wondering how you expect a time delay to operate after the power shuts down to your power supply units.
 

boyd

Oct 7, 2016
64
Joined
Oct 7, 2016
Messages
64
Hi,

It is a joinery workshop. So M1 is a typical machine of about 8 machines. If M1-8 fail to start and I get a 12vdc signal several things will happen.

1: My extractor starts - or continues to run if I have just changed machines within the set time delay.
2: A pneumatic solenoid will operate through an additional control system to physically open a gate in the 100mm dust extraction piping.

If machine one does not operate yet I get 12VDC I will immediately know and be resolving the issue with M1-8.

I have decided to install two solid state relays in each extractor cuircut for neutral and phase. They are cheap. I am also putting in a time(off) delay on the low voltage side, and current/voltage protection in the high voltage side (I might just put in a breaker) Funny, I well know 230VAC can kill but the last job I was on I ended up troubleshooting 3KV lol

As for the time(off) delay I plan to insert two of these:

https://www.aliexpress.com/item/1pc.../1100514896.html?spm=2114.13010608.0.0.rhGwFl

Into the 12vDC side of the extractor control.

I am going to use four of these:

https://www.aliexpress.com/item/1pc...32681597174.html?spm=2114.13010608.0.0.FnRpAF

Thoughts? See problems?

Obviously I am earthing EVERYTHING! Along with a fire security system.
 

Bluejets

Oct 5, 2014
6,901
Joined
Oct 5, 2014
Messages
6,901
If M1-8 fail to start and I get a 12vdc signal several things will happen.

This can never happen.( as drawn)
 

boyd

Oct 7, 2016
64
Joined
Oct 7, 2016
Messages
64
Ok. I smoked my relays! I don't know if its because they are cheap or if 40A is too small for a 230v 2.2KW motor.

First - one of my single phase motors uses a KJD17 (I think) to start. I was unsure how to wire it so just connected the cap and motor (four wires coming out of the motor) in parallel. The SSR exploded and blew a breaker. Wow. Good smoke. Must work out how to wire it???

I connected the other 2.2KW motor in a basic circuit shown in my drawing. The SSR operated once but then fused closed circuit when I removed the 12vdc input. So the motor keeps running and has done with all 3 relays I had spare. Except for one relay which has a resistance of 3k ohms when I input 12vdc.

There is a whole bunch of other stuff in the operation but what has stumped me is why the relays are fusing closed circuit. Too much initial current draw from the motor?

I do plan to install SSRs on the phase and neutral but my initial attempt at getting this running has failed at what I expected to be the easy part :-(

Can anybody please tell me I am wrong in what I have done? And what I should do?

This is the relay

https://www.aliexpress.com/item/1pc...32681597174.html?spm=2114.13010608.0.0.m5ARP5

Uploaded is the basic wiring.
 

Attachments

  • 08121602.JPG
    08121602.JPG
    65.2 KB · Views: 85

boyd

Oct 7, 2016
64
Joined
Oct 7, 2016
Messages
64
Hey so might be talking to myself now because you guys think I am a wolly. Anyway I have bought a bunch of 80A relays.

The ones I bought, latched the first time and then stayed latched!

Except for one. Picture attached. I have wired a single phase motor 230v. This on a single capacitor. Four wires coming out of the motor so I connected them in parallel. Basic terms, the cap and motor winding in parallel as I though was supposed to be.

The picture attached was the result. Direct short!! Now I have looked on the net and am a little confused. I wonder if the KJD 17 switch that has the "extra" terminal is momentary contact only and that there is no centrifugal switch in the motor?

I know I must be sounding like a novice dork but gee. So I cut one of the cap wires. The motor starts, but slower than the other machine I have. Although the other identical machine (extractor) is a two cap motor.

Anyway. Smoke and Bang is always interesting. So here tis a pic. I am looking forward to installing the 80A relays but would still like to get to the bottom of the motor issue.