Maker Pro
Maker Pro

Looking for a signal conditioner

B

BIGEYE

Jan 1, 1970
0
I've got a level transducer that I want to use on a project. The transducer
has a 4/20 mA output equivalent to 0 to 5 metres. Unfortunately the range of
the transducer is too large for what I need. I only need about 4 to 9.8 mA =
0 to 1.8 metres. The receiving instrument is 4/20 mA input = 0 to 100%. My
100% is 1.8 metres and not the 5 metres of the tx.
Is there a signal conditioner available where I could input the 4 to 9.8 mA
and get 4 - 20 mA output, or is there another way (apart from buying a new
tx to the range I require).
TIA
 
H

Herman Family

Jan 1, 1970
0
You don't indicate what sort of receiving instrument you are using. or what
sort of control you have on your level transducer. You basically need to
change the slope parameter on one of them. If your receiver is a dcs, an
sldc, or a plc, there is a decent chance that you could redefine the
bandwidth in the receiver without a lot of trouble.

There are some signal available which convert between various protocols.
One of these might have a range which works for you. Setting your initial
signal up as a voltage (0 to 10 volts) using a resistor might let you change
from 0 to 10 v to 4 to 20 mA, which would give you your range.
Unless you absolutely need the extra precision or absolutely must have the
full 16mA bandwidth, I'd either get a transducer which fits the right range,
or just go with the 9.8 mA maximum signal, rather than modify it.

I'm not so concerned about your ability to fool with it. It's avoiding the
headache for the next guy who has to deal with non standard equipment.

Michael
 
B

BIGEYE

Jan 1, 1970
0
Herman Family said:
You don't indicate what sort of receiving instrument you are using. or
what sort of control you have on your level transducer. You basically
need to change the slope parameter on one of them. If your receiver is a
dcs, an sldc, or a plc, there is a decent chance that you could redefine
the bandwidth in the receiver without a lot of trouble.

There are some signal available which convert between various protocols.
One of these might have a range which works for you. Setting your initial
signal up as a voltage (0 to 10 volts) using a resistor might let you
change from 0 to 10 v to 4 to 20 mA, which would give you your range.
Unless you absolutely need the extra precision or absolutely must have the
full 16mA bandwidth, I'd either get a transducer which fits the right
range, or just go with the 9.8 mA maximum signal, rather than modify it.

I'm not so concerned about your ability to fool with it. It's avoiding
the headache for the next guy who has to deal with non standard equipment.

Michael


It is an analogue readout 0 - 100%
 
I

Iain

Jan 1, 1970
0
BIGEYE said:
It is an analogue readout 0 - 100%

You sure it doesnt have a zero and a span adjustments to let you set the 0
to 100 percent to twhatver loop current you need? Most I've seen have,
rather than rigid 4-20 = 0 to 100.
 
J

Jerry Avins

Jan 1, 1970
0
Iain said:
You sure it doesnt have a zero and a span adjustments to let you set the 0
to 100 percent to twhatver loop current you need? Most I've seen have,
rather than rigid 4-20 = 0 to 100.

Draw a new card for the meter. Your intended use is nearly full scale;
that ought to leave you with enough accuracy.

Jerry
 
D

Dave Slee

Jan 1, 1970
0
BIGEYE said:
I've got a level transducer that I want to use on a project. The transducer
has a 4/20 mA output equivalent to 0 to 5 metres. Unfortunately the range of
the transducer is too large for what I need. I only need about 4 to 9.8 mA =
0 to 1.8 metres. The receiving instrument is 4/20 mA input = 0 to 100%. My
100% is 1.8 metres and not the 5 metres of the tx.
Is there a signal conditioner available where I could input the 4 to 9.8 mA
and get 4 - 20 mA output, or is there another way (apart from buying a new
tx to the range I require).
TIA

Without hesitation, I'd reccomend to anyone who plays with 4-20mA loops,
+/-10V command signals, valve drivers and so on to have one of these in
their toolbox...

Weidmuller WAS4 PRO DC/DC part no. 8560740000

http://www.weidmuller.co.uk/docs/do...&m1=20177&m2=20287&m3=24448&m4=26245&m5=28604

(go to the website for Weidmuller, Downloads, Catalogues & Brochures,
Product Information, Electronics, Analogue signal conditioning, page 28
onwards). Sorry, its big at about 3MB of PDF, but it is well worth having
for reference.

OK, why do I think they are so good? Apart from pulling me out of the brown
smelly just recently, these things will take more or less any voltage or
current signal and linear scale it to more or less any other voltage or
current signal with true three port isolation. They do standard calibrated
ranges like 4->20mA or -10->+10V. They do bipolar current like a +/-10mA
command signal. They run off just about any auxillary supply to hand either
AC or DC. They have span and zero pots for weird sub-ranges of either input
or output. And a killer feature... 10kHz bandwidth with a switchable filter
to slug that to 10Hz bandwidth.

For signal conditioners they are quite pricey (£130 or so each in the UK).
But the beauty is they bodge anything to anything.

As for the brown smelly I mentioned? I'm using some to actually drive
hydraulic servo valves directly. The old controller I have wants to send
+/-50mA PWM current with 500Hz dither and my modern replacement valves with
on-board electronics expect +/-10mA. Yes, I could try setting up a current
divider with parallel resistors across the input to the new valve, but it
was easier just to put one of those conditioners in and set the appropriate
input and output ranges, 10kHz bandwidth and off I went. Got a ground loop
isolation which turned out to be beneficial as a lucky side effect too.

Hope this saves you trawling through many, many catalogues.

Best Regards,
Dave Slee
 
B

BIGEYE

Jan 1, 1970
0
Dave Slee said:
Without hesitation, I'd reccomend to anyone who plays with 4-20mA loops,
+/-10V command signals, valve drivers and so on to have one of these in
their toolbox...

Weidmuller WAS4 PRO DC/DC part no. 8560740000

http://www.weidmuller.co.uk/docs/do...&m1=20177&m2=20287&m3=24448&m4=26245&m5=28604

(go to the website for Weidmuller, Downloads, Catalogues & Brochures,
Product Information, Electronics, Analogue signal conditioning, page 28
onwards). Sorry, its big at about 3MB of PDF, but it is well worth having
for reference.

OK, why do I think they are so good? Apart from pulling me out of the
brown
smelly just recently, these things will take more or less any voltage or
current signal and linear scale it to more or less any other voltage or
current signal with true three port isolation. They do standard calibrated
ranges like 4->20mA or -10->+10V. They do bipolar current like a +/-10mA
command signal. They run off just about any auxillary supply to hand
either
AC or DC. They have span and zero pots for weird sub-ranges of either
input
or output. And a killer feature... 10kHz bandwidth with a switchable
filter
to slug that to 10Hz bandwidth.

For signal conditioners they are quite pricey (£130 or so each in the UK).
But the beauty is they bodge anything to anything.

As for the brown smelly I mentioned? I'm using some to actually drive
hydraulic servo valves directly. The old controller I have wants to send
+/-50mA PWM current with 500Hz dither and my modern replacement valves
with
on-board electronics expect +/-10mA. Yes, I could try setting up a current
divider with parallel resistors across the input to the new valve, but it
was easier just to put one of those conditioners in and set the
appropriate
input and output ranges, 10kHz bandwidth and off I went. Got a ground loop
isolation which turned out to be beneficial as a lucky side effect too.

Hope this saves you trawling through many, many catalogues.

Best Regards,
Dave Slee

Thanks, these look very useful.
 
Top