We have a 3 phase sistem with 380 V betwen phases and 220v phase to
neutral. An electrician was doing a repairation and he just disconect
a neutral wire from a cabinet and conect it a few minutes later and
in that time 3 computers were destroyed, even one of them started to
burn. After that we measure the volts and with tne neutral wire
connected we have 220v betwen phase and neutral and wen we disconect
the neutral we have 500v betwen the same phase and the neutral. Can
any one tell me wat is going on?
Thanks in advance.
Chris.