Hi all

I just salvaged this beast from a broken amplifier and it is absolutely massive in my opinion, I am honestly abit intimidated by it, so I want to make sure I get it right.

18c0b6a09f.jpg

18c0b925a6.jpg


The place where it says:
SEC: 2x50V/6,25A

Are those 6.25 amps per secondary or a combined total?
Depending on the answer for question one, that 6,3AT fuse that is specified on the right.. primary or secondary side(s) and what does the T mean?

Thanks in advance all :)
 
Last edited:

Minder

Apr 24, 2015
3,478
Joined
Apr 24, 2015
Messages
3,478
6.3AT means 6.3a time delay.
It appears to be a fuse for each secondary it would indicate around 630 va which by the size I would think it close.
M.
 

Rixen

Feb 16, 2016
98
Joined
Feb 16, 2016
Messages
98
Alright, 6.25A coupled with a 6.3AT fuse per secondary, got it.

Bonus question, those transformer fuses, are they normally a resettable type?
 

(*steve*)

¡sǝpodᴉʇuɐ ǝɥʇ ɹɐǝɥd
Moderator
Jan 21, 2010
25,510
Joined
Jan 21, 2010
Messages
25,510
There may not be a fuse there at all. It may be a recommendation. The designation suggests a non-resetable fuse.
 

Minder

Apr 24, 2015
3,478
Joined
Apr 24, 2015
Messages
3,478
time delay can also go under Slo-Blo fuse, they can be had in 3AG glass fuse style.