Does anyone know how much current can be pumped through a single pin on a 5 Pin XLR connector? thanx
 

daddles

Jun 10, 2011
443
Joined
Jun 10, 2011
Messages
443
No, but you can estimate it by some measurements. A few months ago I did this for BNC connectors, as there are no specs for BNC power dissipation (i.e., the actual power you can dissipate in the connector). The pins, sockets, and pin-to-socket connection's resistances will be down in the milliohm or sub-milliohm region. The limiter of the connection is probably the wire that is used in the connector, not the connector; this is the case with the typical RG-58/U coax used with BNC connectors. Get a constant current power supply and measure the temperature rise of the connector body with an IR thermometer as a function of current. Use your engineering judgment as to what's an acceptable temperature rise. For the BNC/coax, I decided that I would limit my BNC cables to 5 A continuous DC current, but would allow 10 A for short periods (say, a minute or two).
 

Resqueline

Jul 31, 2009
2,848
Joined
Jul 31, 2009
Messages
2,848
If you're referring to the good old "massive" pin with solder bucket types then here are some common/ general spec's:

Rated current per contact @ 35°C:
3 pole: 16A (max 12 AWG)
4 pole: 10A (max 16 AWG)
5 & 6 pole: 7.5A (max 18 AWG)
7 pole: 5A

Contact resistance: ≤ 3mΩ

Rated Voltage: 50 or 250V AC (depends on brand)

Switchcraft brand seems to be rated a bit lower:
Current Rating (Carry Only): 5A, 125 VAC (4A, 125 VAC on 5 circuit) based on 30°C maximum.
 