The Setup
11 kV comes in from DNO onto a common busbar via our 11 kV CB.
On the same busbar I have 2 CHP alternators. They supply 11 kV onto bus
by way of 415/11000 V step up transformers. Normal operation is for
either or both CHP's running in parallel with DNO.
History
One of the CHP's recently had a catastrophic failure of it's 11 kV
circuit breaker. Prior to the breaker failing, the alternator was
allowed to run as a motor for some 8 minutes.
All repairs have now been carried out and the alternator tested and put
back into service.
Problem
I was in the sub station the other day and noticed that the power factor
meter on our incomer from the DNO was bouncing all over the place, from
about 0.5 lagging to 0.5 leading and was very unstable and erratic. This
also caused our power factor to trip off on unstable power factor. At
the time, both CHP's were running in parallel with the mains.
I shut down the CHP that had the circuit breaker problem as described
earlier, and the power factor stabalised at 0.7 lagging. I reset my
power factor correction and my PF rose to 0.9 lagging and was stable.
Restarted and brought on load the CHP alternator, and again my PF went
crazy. Eventually, shut down the machine and it stabilised again.
Everything is OK when running on mains only or mains in parallel with
the other CHP.
Can anyone advise what may be the problem, how do I diagnose, and how do
I fix.
TIA
11 kV comes in from DNO onto a common busbar via our 11 kV CB.
On the same busbar I have 2 CHP alternators. They supply 11 kV onto bus
by way of 415/11000 V step up transformers. Normal operation is for
either or both CHP's running in parallel with DNO.
History
One of the CHP's recently had a catastrophic failure of it's 11 kV
circuit breaker. Prior to the breaker failing, the alternator was
allowed to run as a motor for some 8 minutes.
All repairs have now been carried out and the alternator tested and put
back into service.
Problem
I was in the sub station the other day and noticed that the power factor
meter on our incomer from the DNO was bouncing all over the place, from
about 0.5 lagging to 0.5 leading and was very unstable and erratic. This
also caused our power factor to trip off on unstable power factor. At
the time, both CHP's were running in parallel with the mains.
I shut down the CHP that had the circuit breaker problem as described
earlier, and the power factor stabalised at 0.7 lagging. I reset my
power factor correction and my PF rose to 0.9 lagging and was stable.
Restarted and brought on load the CHP alternator, and again my PF went
crazy. Eventually, shut down the machine and it stabilised again.
Everything is OK when running on mains only or mains in parallel with
the other CHP.
Can anyone advise what may be the problem, how do I diagnose, and how do
I fix.