Ignoramus30170 said:
I have two devices that left me completely stumped. They are
Associated Research made devices. One seems to be a high voltage hypot
tester. Another has 1/0 welding cable attached to it. At least one is
called HyJoule.
Anyway, I am lost as to just what could be tested with a 1/0 welding
cable (about 100 ft or so).
They are both the size of a under the desk refrigerator and VERY
heavy, maybe 200-300 lbs each.
i
Hi Ig,
I've used gear like this on high voltage cable fault location. From your
limited description, I can't tell you exactly what you have there, but I can
tell you the sort of gear used on high voltage cable faults.
Testing a new or repaired cable needs high voltage DC , not much current
required, typically milliamps once the cable is charged.
When you are trying to locate a fault, you need some way to get a primary
location. This can be an impulse current reflection measuring device which
shows you a picture of the wave as a hv capacitor is dicharged into the
fault. Typically, you do this down a good core, then to the faulty core and
compare to see where the waves deviate.
An older method involved a high voltage bridge, and sometimes this required
a very heavy cable to connect the far end of a good core to the far end of
the faulty core. We have a cable that is like what you describe for a
particlarly strange setup in one of our substations.
Once you have a primary location, you go to that point on the cable and
listen for the fault with senstive listening equipment while the the
capacitor is discharged repeatedly into the fault.
When the cable is buried under a city street, it can be quite difficult to
hear the fault. It can also happen that the original fault was cleared so
quickly that the outer sheath of the cable is still intact. This means that
the noise is inside a lead pipe, and even if you can hear it, you can't
pinpoint the exact position of the fault. The answer is to discharge a very
large capacitor - high joule - into the cable, the resulting high energy
burns the cable down and makes the fault easier to find. I think the second
box you have is a burn down unit.
Both these units you have will kill you as quick as look at you. Even if
they have not been used in a while, if the capacitors were not dicharged and
earthed properly, they will bite. Be careful !
regards,
John