is there any street lighting engineers here

A

Andy Smith

Jan 1, 1970
0
What is the consensus regarding whether to use a loop-in / loop-out wired
system as opposed to using cable joints to spur into lighting columns
 
S

SQLit

Jan 1, 1970
0
Andy Smith said:
What is the consensus regarding whether to use a loop-in / loop-out wired
system as opposed to using cable joints to spur into lighting columns

Personally I never liked splicing underground. When the wires are pulled up
to the poles and then spliced in the pole, I believe those connections will
last better. I have done it the other way, they still work, just did not
like the idea.
 
M

Miles

Jan 1, 1970
0
Andy Smith said:
What is the consensus regarding whether to use a loop-in / loop-out wired
system as opposed to using cable joints to spur into lighting columns

I only have a small amount of experience in this but I'd say that the
loop-in, loop-out should have a higher reliability and lower lifecycle cost
due to the fact that underground joints do create a weak point which can
(and does) fail later in the life of the cable system.
 
A

Andy Smith

Jan 1, 1970
0
I only have a small amount of experience in this but I'd say that the
loop-in, loop-out should have a higher reliability and lower lifecycle cost
due to the fact that underground joints do create a weak point which can
(and does) fail later in the life of the cable system.

yes I also agree, however cable jointing has become more advanced than it
was a few years ago, with some very sturdy jointing kits availible.
Also, there is a possibility of course, that on long runs of cable (along a
highway for example) the main cable will be of a large CSA (e.g. 120mmsq)
providing a low impedance earth loop impedance return path and therefore a
relatively high fault current.

The joint spur cable into the lighting column will only need to be of small
CSA.

The concern is that should an earth fault occur in the column, the spur
cable would carry the burden of the fault current and could overheat or
completely fail.

Of course, it would not be possible to use the same CSA as the main cable
run because it would be impossible to terminate such a large conductor into
the column. the answer would be to add fuse or circuit breaker protection
to the smaller cable, but joints do not allow this facility.

In the UK it is common to use loop-in / loop-out wiring. what is the norm
in other countries??

Any comments welcomed, as i am putting a project proposal together soon.
 
A

Andrew Gabriel

Jan 1, 1970
0
In the UK it is common to use loop-in / loop-out wiring. what is the norm
in other countries??

Presumably this means a column felled by a car is likely to disable
a whole line of lamps. This is not what I normally observe, i.e. a
felled column does not normally disable the rest of the lamps.

I've seen motorway lighting in the UK where the joint spur is in
a ground inspection chamber some ~6' from the base of each column.
In that strech, a lorry felled around 5 columns which are still
missing, but the line of lamps either side is still working fine.
 
J

Jb

Jan 1, 1970
0
Have to disagree, loop in loop out is usually only on private cables. UK
lighting is by 4mm hybrid cable jointed to the nearest LV main.
 