I'm seeking the opinion of a someone having experience with the Lenel
Onguard system to help me in resolving a problem with false forced
open alarms on a new install.
Here's the situation: We just installed 6 doors using LNL-1320
controllers, electrified strikes, and PIR for REX. The problem is that
we're getting numerous false forced open alarms on exit. We've had the
installers working to resolve the problem. It's gotten better, but
it's not fixed.
Initially, the PIRs were set with a 6 second hold time. The scenario
is two people standing under the PIR (REX is active), one opens the
door and leaves (REX is still active), the door closes (REX is still
active), the other opens the door to leave (REX is still active) and
gets a forced open alarm. If the REX is allowed to cycle the alarm
does not occur. Clearly the LNL-1320 requires one REX transition per
door opening.
The installer's solution was to shorten the PIR hold time to the
minimum of .25 seconds. That fixed the original problem. The new
problem is that if a person pauses for just an instant before opening
the door a false forced open results because the REX goes inactive.
The solution to that was to increase the PIR hold time back to 6
seconds and change the door status contact to a dual switch. The
second circuit being used to interrupt the REX when the door is
opened. This has the effect of cycling the REX when the door is
opened, thus satisfying the one door event per REX requirement of the
LNL-1320.
It works most of the time. But every once and a while a false forced
open will occur for no apparent reason. It's my opinion that having
the two switches (door status and REX interrupt) co-located results in
a timing problem for the 1320. Most of the time it gets it right, but
sometimes it sees the REX drop before the door status opens. I believe
the correct wiring solution is to place a separate REX interrupt
switch at the top of the door about 10" out from the hinge. This will
insure that the REX is interrupted after the door status switch
(located at the strike) registers door open.
A firmware solution (to allow multiple door opens per REX) is also
possible, but somehow I don't think that will happen.
So, does anyone have any opinions on this? And how should the LNL-1320
be used with a PIR REX device?
Thanks in advance,
---Scott.
Onguard system to help me in resolving a problem with false forced
open alarms on a new install.
Here's the situation: We just installed 6 doors using LNL-1320
controllers, electrified strikes, and PIR for REX. The problem is that
we're getting numerous false forced open alarms on exit. We've had the
installers working to resolve the problem. It's gotten better, but
it's not fixed.
Initially, the PIRs were set with a 6 second hold time. The scenario
is two people standing under the PIR (REX is active), one opens the
door and leaves (REX is still active), the door closes (REX is still
active), the other opens the door to leave (REX is still active) and
gets a forced open alarm. If the REX is allowed to cycle the alarm
does not occur. Clearly the LNL-1320 requires one REX transition per
door opening.
The installer's solution was to shorten the PIR hold time to the
minimum of .25 seconds. That fixed the original problem. The new
problem is that if a person pauses for just an instant before opening
the door a false forced open results because the REX goes inactive.
The solution to that was to increase the PIR hold time back to 6
seconds and change the door status contact to a dual switch. The
second circuit being used to interrupt the REX when the door is
opened. This has the effect of cycling the REX when the door is
opened, thus satisfying the one door event per REX requirement of the
LNL-1320.
It works most of the time. But every once and a while a false forced
open will occur for no apparent reason. It's my opinion that having
the two switches (door status and REX interrupt) co-located results in
a timing problem for the 1320. Most of the time it gets it right, but
sometimes it sees the REX drop before the door status opens. I believe
the correct wiring solution is to place a separate REX interrupt
switch at the top of the door about 10" out from the hinge. This will
insure that the REX is interrupted after the door status switch
(located at the strike) registers door open.
A firmware solution (to allow multiple door opens per REX) is also
possible, but somehow I don't think that will happen.
So, does anyone have any opinions on this? And how should the LNL-1320
be used with a PIR REX device?
Thanks in advance,
---Scott.