Metro said:
Looks like there could be problems ahead. Had to happen I suppose. Not
enough thought went into it........

rooftop-solar-panels-overloading-electricity-grid

Isn't that vindication of the program to install them;they can meet
demand, The overloading infrastructure problem should be laid at the
feet of the various state governments who ratted the infrastruture
refurbishfund that all the various electrical authorities had put aside.
That is why you are not going to pay 30%+ on your electricity bills.
 
T

Trevor Wilson

Jan 1, 1970
0
P

Phil Allison

Jan 1, 1970
0
"Trevor Wilson"
**Care to explain how grid connected inverters are capable of feeding MORE
than mains Voltage (whether it is a nominal 230VAC or 240VAC) into the
grid?


** No current would flow from the inverter UNLESS it put out more volts than
were otherwise on the incoming line.

The story is mostly a beat up of something quite minor that happens only in
rural locations with long supply lines and hence relatively high source
impedance AC supplies. Such locations already suffer wider variations in the
AC voltage.

BTW:

High AC voltages mostly affect the lifespans of ordinary, 240 volt rated
incandescent lamps - which are banned from sale anyhow.


.... Phil
 
M

Metro

Jan 1, 1970
0
Phil Allison said:
"Trevor Wilson"


** No current would flow from the inverter UNLESS it put out more volts
than were otherwise on the incoming line.

The story is mostly a beat up of something quite minor that happens only
in rural locations with long supply lines and hence relatively high source
impedance AC supplies. Such locations already suffer wider variations in
the AC voltage.

BTW:

High AC voltages mostly affect the lifespans of ordinary, 240 volt rated
incandescent lamps - which are banned from sale anyhow.


... Phil
Just to be pedantic. Not all incandescent lamps are banned from
sale.......For instance.

http://lightingpro.com.au/catalog/index.php?cPath=21&RD=LPHomTxtLightGlobes

Pity though, nothing like the old 60w pearl.
 
P

Phil Allison

Jan 1, 1970
0
"Tony Simpleton"
What's that supposed to mean:

'Mr Hart said the size of conductors and cables in the streets would have
to be upgraded "so it can handle lots of solar, versus times when
there's lots of load and no solar".'


** Makes perfect sense.

If there is adequate copper, then voltage drop problems vanish.


The problems I see are rapid changes of insolation in areas where PV
supply is dominant (e.g. clouds moving fast). It takes time for the flow
from the power station to react.


** My god - you really are off with the fairies.



.... Phil
 
J

Jeßus

Jan 1, 1970
0
incandescent lamps - which are banned from sale anyhow.

Only last Tuesday, I spotted a shelf full of incandescent bulbs on
sale at Coles in Launceston.
 
T

Trevor Wilson

Jan 1, 1970
0
Only last Tuesday, I spotted a shelf full of incandescent bulbs on
sale at Coles in Launceston.

**There are still a large variety of IC lamps available. Fancy shapes,
odd bases, halogens and others.
 
P

Phil Allison

Jan 1, 1970
0
"Jeßus"

"Phil Allison"
Only last Tuesday, I spotted a shelf full of incandescent bulbs on
sale at Coles in Launceston.


** What a vile, over snipping turd you are.

My original comment was:

"High AC voltages mostly affect the lifespans of ordinary, 240 volt rated
incandescent lamps - which are banned from sale anyhow. "

FFS " ordinary, 240 volt rated " = GLS, non halogen.



.... Phil
 
J

Jeßus

Jan 1, 1970
0
** What a vile, over snipping turd you are.

And what's worse, no remorse about it either.

Fortunately for turds like myself, crimes against Usenet do not fall
under the ICC's jurisdiction, else I'd fully expect to be extradited
to The Hague.
My original comment was:

"High AC voltages mostly affect the lifespans of ordinary, 240 volt rated
incandescent lamps - which are banned from sale anyhow. "

FFS " ordinary, 240 volt rated " = GLS, non halogen.

OK. So what is 'GLS'?
 
T

Trevor Wilson

Jan 1, 1970
0
And what's worse, no remorse about it either.

Fortunately for turds like myself, crimes against Usenet do not fall
under the ICC's jurisdiction, else I'd fully expect to be extradited
to The Hague.


OK. So what is 'GLS'?

**General Lighting Service.
 
M

Metro

Jan 1, 1970
0
Phil Allison said:
"Tony Simpleton"


** Makes perfect sense.

If there is adequate copper, then voltage drop problems vanish.
That's the question. Is there adequate copper? I think maybe not with all
the upgrading going on throughout the Western Suburbs of Sydney
 
J

John Tserkezis

Jan 1, 1970
0
Metro said:
Looks like there could be problems ahead. Had to happen I suppose. Not
enough thought went into it........

Did you miss the fact that the author of that 'The Australian' article
is a complete knob, and has no idea on how the grid works?
He invents terminology, quotes others out of context, and quotes
installers who have equally no clue on how anything works at all.

The Internet is loaded with lots of information on how the power grid
works in general, and how the different forms of solar controllers work,
AND how they interact with the grid.

I would suggest reading one of those, because *this* article is NOT
one of them.
 
M

Metro

Jan 1, 1970
0
John Tserkezis said:
Did you miss the fact that the author of that 'The Australian' article is
a complete knob, and has no idea on how the grid works?
He invents terminology, quotes others out of context, and quotes
installers who have equally no clue on how anything works at all.

The Internet is loaded with lots of information on how the power grid
works in general, and how the different forms of solar controllers work,
AND how they interact with the grid.

I would suggest reading one of those, because *this* article is NOT one
of them.
--
The author also quoted "One of Australia's biggest electricity network
providers, Ausgrid, yesterday warned that there was a "significant
likelihood" that costs would have to rise because of the impact of the solar
photovoltaic cells." All a ruse I suppose. To me what you say is most
probably correct in theory. But not in practice. The condition of the
network aint so good. No forethought to future needs and technology was
given by the planners a few years ago and I think we are starting to pay for
it now. It's not only copper but also lack of maintenance to pad mounts,
pole mounts and general hardware upgrades. But then I didn't go to uni to
learn all this. I just work with it!
 
D

Dimmer

Jan 1, 1970
0
Article and quotes by CEOs seem complete rubbish to me as a layman. Here's
my take: The supply from a normal solar panel is unlikely to exceed what a
home uses unless of course everything if off and the people are away. So
given that usually a user of solar panels will simply be *reducing* the call
on the mains supply, the net power drawn through the gird will be less, so
shortcomings in copper should not be a problem.

True there wll certainly be fluctuation when there is intermittent cloud
cover, but on the whole that should be 'normal demand' punctuated by reduced
demand. Not normal demand punctuated by increased demand!
 
J

John Tserkezis

Jan 1, 1970
0
TonyS said:
On second thought I got a bit of an idea where the problem may come to
surface. I have no experience in grid technology, so correct me if I am
wrong.
First of all I must say, people do try to avoid heavy usage when the sun
is shining, cause they can sell their electricity for about double of
what they would pay. Which means they do feed into the net as much as
they can in day time.

Not really, or at least, they don't have any say in that.

In the following hypothetical, (I'm assuming that ALL homes on a given
isolated grid, also have solar assistance). It won't happen in real
life, but this is just for the sake of this explanation.

If ONE home chooses to stop using ALL possible power during a peak
demand interval, AND, no-one else does that, THEN, their system has the
*potential* (owing to light and battery power availability) to supply
its full capability into the grid, and get paid for their bit.
This is of course assuming the remaining homes have a net negative
generation, that is, even accounting for THEIR own solar systems, they
still use MORE than what they generate themselves. In other words, they
still draw something from the grid.

If ALL solar homes had the same idea (power off everything and let
their solar systems pump power into the grid), then, NO-ONE would
pumping power into the grid - their controllers simply will NOT let it.
There are safety limits built in that prevent over voltage from
happening. This entirely debunks the "solar overloads the wiring"
statement, as well as the amount of copper.
The voltage at a transformer would always be at the higher end to cater
for the copper losses to be expected farther down the line.

It depends. Although the "grid" operates as a large-scale entity, it
does indeed have some localised effects. And it NEEDS this, because
even though the "grid" operates with some self-regulation as far as
voltage goes (power stations vary up and down according to demand, and
voltage is a good indicator of what the load is.
There are quite high variations on the local level, because one suburb
may have no air-cons, and the next door suburb may have them all. And
the larger scale grid feeds them both.
To ensure YOUR grid voltage stays within "acceptable" limits, there
are local transformers that change taps to offer some control for this.

In the hypothetical that solar systems feed "too much" power into the
grid (they won't, but let's say they do anyway), the transformer will
switch to account for that, so less comes from the larger scale grid,
and the local solars can supply a chunk of power.

This will not magically "stress" the copper, because the copper isn't
carrying any more current that it's capable of ANYWAY.
If, however, there are a number of powerful solar supplies feeding in
along that transmission line, much of the current goes the other way,

Firstly, there is no "other way". Due to normal losses in copper,
YOUR solar system has MOST effect closest to you, and the LEAST effect
furthest away from you. The change YOUR solar box has on the whole is
rather local.
and the voltage drop due to copper losses could even ADD to the grid
voltage.

Again, only locally, AND if the box lets it. If the grid voltage is
ALREADY high, YOUR system will NOT push bucketloads of power into the grid.
So instead of the usual voltage drop due to copper losses we
would have a gain. The only way to avoid this reversal would be to use
more copper or less solar.

:) Congratulations, you've just turned a positive into a negative.
What you're saying is a GOOD thing, and does not require "fixing". It's
also the cheapest and most effective way of addressing load.

Take the far southern end of Victoria for instance. They're at the
end of a long copper line, ant the wrong end of the power generation
side, so there are significant losses. They have increasing peaks loads
due to air cons and huge TV sets.
Increasing copper would help, but ultimately, no-one is going to pay
millions so a tiny town can have air cons and TV sets.
What they're doing now, is using wind power to supplement peak power.
So that droop due to load goes away, because the wind generators are
taking up the slack. This is a GOOD thing.
Of course, they want to whine about the noise, and they have every
right to do that. The easiest way to fix that is to get THEM and THEM
ALONE to pay the millions or billions for the copper upgrades. As long
as everyone else doesn't have to pay, I'm quite happy to let them have that.
As far as fluctuations are concerned, I think we'd need a lot more solar
power, like a double digit share, to see an impact on the grid voltage
or frequency.

That theory would fail, mainly because it's these huge peaks (aircons)
that need LOTS of power generation over short periods.
Generating this class of power is expensive, but in above example,
it's still cheaper than copper.
Again, this is for long haul copper, local systems will see no
(worthwhile) gain in copper upgrades.
 
J

John Tserkezis

Jan 1, 1970
0
TonyS wrote:

There's a few misconceptions here, I'll address them individually.
I don't see the point of the assumption. There will always be a number
of houses with PV producing more than they use, especially on days where
no A/C is needed.

Yes, my hypothetical examples where the extremes, and only for the
purposes of explanation.
The line loss will lift the voltage.

Yes, but there are limits were it'll no longer supply power to the grid.
Should the upper voltage limit be reached, some of the inverters will
cut out first and the voltage will not rise above he limit.

There are no "cut outs". It's a sliding scale, it could put full
power into the grid, it could put in a couple of amps, it could be less.
It's not an on/off arrangement.
But, depending on the hysteresis of the sensing circuits, they will switch on again.

As above, it's not like that.
An inverter that switches off turns into a sink what used to be a
source and so not only takes away feeding current but also adds some
load and so amplifyies the effect.

No, that doesn't happen either. The controller doesn't take from the
grid any more than it needs to self-manage, and it's not a lot.
If you have flat batteries and no sun, the batteries stay flat.
Depending on a lot of factors and
inverter design I could imagine some oscillation happening here.

None of that either. You're using faulty assumptions.
Modelling this situation is difficult and we will wait and see if it can
happen.

It hasn't, it isn't, and it won't.
In any case, it's not good as a switched off inverted defeats the
purpose of the PV system and oscillations, God knows...

Not even then. It never behaves as an inverter that you may be
familiar with. In case of a blackout, the system shuts down and does
nothing (same under brown-out conditions too). You may have fully
charged batteries in a fucking stinking hot day, and you STILL won't
have any power to charge your phone.
Never knew that. Are those solid state switches?

Relays, I've out of that game for a long time so I'm not sure if
things have changed, but it appears the major changes are around *when*
the taps are changed, rather than *how*.
I don't doubt that but I think in the article the assumption was that
too many PVs are feeding. If you got more sources than sinks the net
effect is source, with the above mentioned possible effects.

And that's where the article fails. If EVERY person on the planet was
connected to the grid AND had a solar setup, then the ONLY difference
you'd notice compared to the current state of affairs is the Return On
Investment time.
Each person would be feeding a LOT less from their PV setups into the
grid.
There would be no cable issues (actually, in some cases it would
IMPROVE the heavy loading issues).
The result would be nothing else than everyone paying lots of money
for, well, very little.

And I say the above because grid supplied power (baseline is coal) is
significantly cheaper than solar.
Well the downside is, if PVs switch off and assuming nothing else bad
happens, the investment would still be a waste of money (taxpayers money
too). The owners might not even notice, only wonder why the power bill
doesn't go down!

Ah, well done. :) You've picked that up.
What I meant was that sudden solar PV changes won't cause problems at
the generator side yet, due to the small scale.

As I've said, they don't do changes like that, it's a sliding scale,
there is nothing abrubt about it.
 
D

David

Jan 1, 1970
0
"Trevor Wilson"


** No current would flow from the inverter UNLESS it put out more volts than
were otherwise on the incoming line.

Not true in AC system. In an AC power system, real power flow is
determined by the load angle between the generator and the load. Voltage
level differences determines reactive power flow. Quite possible to have
a generator (invertor) supplying real power, but absorbing reactive power.

David
 