Not sure if this fits in exactly with the theme of this forum, but this is where I already have an account, so I'm hoping it'll work out.

At my workplace we have two bathrooms on the same circuit. This circuit breaker keeps getting tripped a lot recently. Each bathroom has one overhead light, one bathroom exhaust fan, one Xcelerator hand drier, and a fan-forced wall mounted heater. I replaced the heater in one bathroom approximately a year ago, and I replaced the heater in the second bathroom a few months ago. The tripping started after replacing the second heater, which I noticed was rated at a higher voltage (and presumably amperage, but not sure). It is a 20 amp breaker switch. Both heaters are the same and they say 120 volt and 12.6,9.4,6.3,3.1 amps (1500,1125,750,375 watts). I assume the different amperage ratings are for the different settings on the heater, it has a knob that goes up to 6.

Of course easy math shows that two 12.6 amp heaters are more than the 20 amp breaker. I tried purposely tripping the breaker as a test, by turning both heaters to max, both lights and fans on, and triggering both hand driers at once, but everything stayed on during that test.

That's about all I know. So I'm just looking for some advice on how I could fix this.

Thanks,
Marc
 

davenn

Moderator
Sep 5, 2009
14,271
Joined
Sep 5, 2009
Messages
14,271
hi Marc

Tho you may get reasonable info on something like that on a forum
it would be very difficult to give quality info due to not being onsite to see and test the actual fault

This really requires you to employ a qualified electrician to sort out something like this :)


cheers
Dave
 

Arouse1973

Adam
Dec 18, 2013
5,178
Joined
Dec 18, 2013
Messages
5,178
Not sure if this fits in exactly with the theme of this forum, but this is where I already have an account, so I'm hoping it'll work out.

At my workplace we have two bathrooms on the same circuit. This circuit breaker keeps getting tripped a lot recently. Each bathroom has one overhead light, one bathroom exhaust fan, one Xcelerator hand drier, and a fan-forced wall mounted heater. I replaced the heater in one bathroom approximately a year ago, and I replaced the heater in the second bathroom a few months ago. The tripping started after replacing the second heater, which I noticed was rated at a higher voltage (and presumably amperage, but not sure). It is a 20 amp breaker switch. Both heaters are the same and they say 120 volt and 12.6,9.4,6.3,3.1 amps (1500,1125,750,375 watts). I assume the different amperage ratings are for the different settings on the heater, it has a knob that goes up to 6.

Of course easy math shows that two 12.6 amp heaters are more than the 20 amp breaker. I tried purposely tripping the breaker as a test, by turning both heaters to max, both lights and fans on, and triggering both hand driers at once, but everything stayed on during that test.

That's about all I know. So I'm just looking for some advice on how I could fix this.

Thanks,
Marc

Is the breaker an RCD type Marc?
Adam
 

Externet

Aug 24, 2009
892
Joined
Aug 24, 2009
Messages
892
Disconnect/disable any item that was in use at the moment of breaker tripping; preferable the suspect new hand dryer to confirm if the behavior persists or not.
If power disruption persists, That dryer circuit can be assumed healthy.

Move the wiring in the breaker box to another equal-rating breaker and evaluate for a while.
 

Tha fios agaibh

Aug 11, 2014
2,253
Joined
Aug 11, 2014
Messages
2,253
Bob's right, your circuits are overloaded.
Even two 20a breakers is probably not enough.
Hire an electrician to make it right. (Gfci protection and applicable codes.)
 

davenn

Moderator
Sep 5, 2009
14,271
Joined
Sep 5, 2009
Messages
14,271
Bob's right, your circuits are overloaded.
Even two 20a breakers is probably not enough.
Hire an electrician to make it right. (Gfci protection and applicable codes.)

which is what I suggested a number of posts ago
for everyone's safety, this thread is closed
 